How to find the IP address of a third party BACnet device
  • How to find the IP address of a third party BACnet device
  • David_Purser
    David_Purser
  • JonGreen
    JonGreen
  • Carl_Slack
    Carl_Slack
‎2018-09-06 10:44 AM
Last Updated: Administrator CraigEl Administrator ‎2022-12-08 05:32 PM
After a find new BACnet devices in Continuum or EBO, 3rd party devices may come in and that we do not know the IP address of.
Andover Continuum, EcoStruxure Building Operation
  • Continuum Cyberstation BACnet Operator Workstation
BACnet devices IP addresses in Continuum explorer and EBO are encoded in HEX per BACnet Standard. BACnet IP addresses in BACnet are described as BACcnet MAC address.
3rd party IP level device is already in the BACnet side of Continuum, the IP address in HEX located as BACnet MAC address.
Right-click and edit the third party device and use the BACnet MAC address to decipher. That is the IP address plus the port used to communicate
For instance:
The BACnet MAC address on the device editor is 0A9F1ACFBAC0
That would be 0A = 10, 9F=159, 1A=26, CF=207
 The IP address would be 10.159.26.207 and BAC0 is 47808 on the port.
If you have exported to Excel and need a solution to covert, please reference IP address from BACnet MAC Address (SBO & Continuum)