Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

How to create a workspace with a banner and a TGML graphic as the home page.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to create a workspace with a banner and a TGML graphic as the home page.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis
  • CraigEl
    CraigEl
  • Mahmoud_Sayed
    Mahmoud_Sayed
  • DavidFisher
    DavidFisher
  • sesa177673
    sesa177673
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
3321 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to create a workspace with a banner and a TGML graphic as the home page.

Picard Product_Support
‎2018-09-06 11:32 AM

Last Updated: Guinan RandyDavis Guinan ‎2023-08-01 08:19 AM

Issue

How to create a workspace with a banner and a TGML graphic as the home page. 

Product Line

EcoStruxure Building Operation

Environment

Building Operation Workstation

Cause

A graphical overview of a building or area containing a number of buildings can be a logical way for a customer to navigate around a site in Workstation.

Resolution

  1. Preparation
    1. Create a folder to contain the graphics and banners to be used.
  2. Create a Panel object
    1. Right-click the folder and select New->Panel.
    2. Set the initial path (ie. the home page) to the desired graphic.
      Panel settings.png

       
    3. Add a graphic pane to the panel.
    4. Edit the graphic pane and select the banner graphic to be used.
    5. Set the desired layout settings such as Default dock position to Top.
      Graphic Panel Settings.png

       
  3. Create a workspace
    1. Click on the control panel icon. Select User Accounts - Account Management and then under the Workspaces section click on Add.
    2. Select the desired security and authority settings.
    3. Add a Panel Pane to Workspace.
    4. Edit the Panel Pane and set the initial path to the Panel object created in step 2.
      WorkSpace Settings.png

       
  4. Assign the workspace to a user group
    1. Under the Select User accounts - Account Management menu in the control panel select the User Group that is to use this workspace.
    2. Edit the User Group and go to the Workspaces tab.
    3. Highlight the appropriate workspace and add it to the Select Workspaces pane by clicking on the arrow.
      User Group.png

       
  5. Test the workspace
    1. Log in with the appropriate user and confirm the layout is as desired.StartPage for graphic user.png
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (2)
  • Find more articles tagged with:
  • 11101
  • MahmoudSayed23
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore