How to create a log file for troubleshooting video integration issues in Continuum

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to create a log file for troubleshooting video integration issues in Continuum
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • Alan_Wood
    Alan_Wood
  • BillNeville
    BillNeville
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2122 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to create a log file for troubleshooting video integration issues in Continuum

Picard Product_Support
‎2018-09-06 02:12 PM

Issue

There is a need to get logging details for troubleshooting video integration issues in Continuum.

Product Line

Andover Continuum

Environment

  • Continuum
  • Windows XP
  • Windows Vista
  • Windows Server 2003
  • Windows Server 2008

Cause

There is an issue with the video integration and there are specific instructions to enable video troubleshooting in Continuum.

Resolution

Continuum versions 1.9x and above contain a helpful tool for troubleshooting video integration issues

To enable video logging, follow these instructions:

  1. Shut down Continuum on the Cyberstation you will use to create the log file
  2. Using Windows notepad, edit the file log4net.config located in C:\Program Files\Continuum
    At the bottom of the file locate the following text: 
  3. <root>

    <level value ="WARN"  />

Change WARN to DEBUG (Ex. level value ="WARN" ---> level value ="DEBUG" )

From the pull down menu, File> Save and close the file

        4.Start Continuum and test one isolated procedure at a time (Ex. video isn't displaying on alarm)

        5. Email the video.log file from the C:\Program Files\Continuum folder to the support engineer for analysis

Note: Make a copy of the video.log file ( to save the file ) and then delete the original. A new video.log file is created each time Continuum is started with the level value="DEBUG" set

Video log changes for 1.92/1.93/1.94

The instructions to enable the video.log are the same as for 1.91, however the results have been broken into a number of different files

VideoAdmin.log - used for configuration 

AccVideoRecordingServc.log - used for camera learn

VideoLayout.log - used for video layout 

AlarmView.log - used for video alarms

Easiest way to see what file was written to is to sort the Windows folder by the Type column and check the txt file(log) dates

Note: In Microsoft Vista or Windows Server 2008, if account control is not disabled the video log files may get written to "C:\users\username\AppData\Local\VirtualStore\Program Files\Continuum"

Caution: Once the debugging process has been completed, go back into the log4net.config file and edit the file.

  1. Change the DEBUG to WARN (Ex. level value ="DEBUG" ---> level value ="WARN")
  2. From the pull down menu, File> Save and close the file

This will stop the files from growing too large.

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 4483
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore