How to control an output with one or more inputs.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to control an output with one or more inputs.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • AdamSteele
    AdamSteele
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
4168 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to control an output with one or more inputs.

Picard Product_Support
‎2018-09-10 12:49 PM

Last Updated: Guinan AdamSteele Guinan ‎2023-09-13 11:29 PM

Issue

How to control an output with one or more inputs.

Product Line

EcoStruxure Security Expert

Environment

Security Expert

Cause

Unsure how to program one or more inputs to directly control an output.

  • Input Control Output

Resolution

The below guide details how to use an Input to activate an Output on Security Expert and SP-C-WEB systems. An output can be assigned to the Input Type and to the Input allowing many to one and one to many configurations.

 

In order for an Input to activate an Output it needs two things:

  1. To be inside an always armed area - This can be an Automation/Dummy area with its only purpose being to activate the output.
  2. To have an Input Type that tells it to activate an Output

 

Single/Multiple Input Activating the same Output
If one or more inputs are required to activate the same output, this output can be defined by the input type. The below is a simple scenario where when the Input turns ON the Control Output turns ON, when the Input turns OFF the Control Output turns OFF. Other types of output activations can be configured if required.

  1. Creating the Area
    1. Navigate to Programming > Areas
    2. Add a new area and name it Automation Area, set the Entry and Exit Delay Times to 0. All other settings can be left default.
  2. Creating the Input Type
    1. Navigate to Programming > Input Types. Create a new Input Type
    2. Set the Control Output to the required output
    3. Under Options 2 enable the required control options for your scenario e.g. to have the output follow the input exactly enable Activate Control Output on Alarm and Deactivate Control Output on Restore. To have the output activate for a time simply enable Activate Control Output on Alarm and set the Activation Time under the General tab of the Input Type Menu (Control Output Time)
      1. For more details on the option see The difference between using "Control Output" and "Input Control Output"
    4. Set any other options that may be required
  3. Configuring the Input
    1. Navigate to Programming > Inputs select the Input and set the following:
    2. Set the Area to the Automation Area created in Step 1
    3. Set the Input Type to the Input Type created in Step 2
  4. Testing
    1. Check for any related health status messages that need to be resolved
    2. Arm both portions of the Area
    3. Activate the Input to confirm Output Activates

 

Multiple Inputs Activating Different Outputs
When multiple inputs are required to activate different outputs, one input type can be used and the outputs can be defined at each input. The below is a simple scenario where when the Input turns ON the Control Output turns ON, when the Input turns OFF the Control Output turns OFF. Other types of output activations can be configured if required.

  1. Creating the Area
    1. Navigate to Programming > Areas
    2. Add a new area and name it Automation Area, set the Entry and Exit Delay Times to 0. All other settings can be left default.
  2. Creating the Input Type
    1. Navigate to Programming > Input Types. Create a new Input Type
    2. Under 'Options 3' enable the required control options for your scenario. e.g. to have the output follow the input exactly enable Activate Input Control Output on Alarm and Deactivate Input Control Output on Restore. To have the output activate for a time simply enable Activate Input Control Output on Alarm and set the Activation Time at the Output itself
      1. For more details on the option see The difference between using "Control Output" and "Input Control Output"
    3. Set any other options that may be required
  3. Configuring the Input
    1. Navigate to Programming > Inputs select the Input and set the following
    2. Set the Control Output to the appropriate Output
    3. Set the Area to the Automation Area created in Step 1
    4. Set the Input Type to the Input Type created in Step 2
  4. Testing
    1. Arm both portions of the Area
    2. Activate the Input to confirm Output Activates
Labels (1)
Labels:
  • EcoStruxure Security Expert
Tags (3)
  • Find more articles tagged with:
  • 19348
  • AdamSteele21
  • AdamSteele23
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore