Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

How to configure a user to be able to arm and disarm the entire site using the SX-KLCS-B Keypad

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to configure a user to be able to arm and disarm the entire site using the SX-KLCS-B Keypad
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • AdamSteele
    AdamSteele
  • BillNeville
    BillNeville
  • RobertAndriolo
    RobertAndriolo

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2944 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to configure a user to be able to arm and disarm the entire site using the SX-KLCS-B Keypad

Picard Product_Support
‎2018-09-11 03:08 PM

Issue

How to configure a user to be able to arm and disarm the entire site using the SX-KLCS-B Keypad.

Product Line

Security Expert

Environment

  • Security Expert
  • SX-KLCS-B Keypad

Cause

Unsure how to program Security Expert to allow control of multiple Areas from one PIN code entry.

Resolution

Below are instructions for how to configure Security Expert to arm/disarm a group of Areas whenever a particular code is entered at the keypad.

v4.2.201

There was a new Function Code added in v4.2.201 that allows easier setup of arming/disarming from a keypad. This only allows controlling a Door, Area or Output with this function code. You aren't able to disarm an Area Group but you are able to select multiple Areas with the same Function Code which will provide the same result.

  1. Navigate to the Sites > Function Codes.
  2. For each Door where you want to use the Function Code, you must add the Function Code in the Function Codes tab of Programming|Doors.
  3. You must also have controller firmware 2.08 b780 or later.

v4.2.194.7

  1. If there is not already a System or Automation Area, one will need to be created. This Area will not report to monitoring, or activate bell outputs onsite. The Area is for internal automated functions within Security Expert. Set the Entry and Exit time to 0 for the Automation Area.
  2. Create an Area Group that includes all the Areas you would like to Arm/Disarm.
  3. Create a Virtual Output (example name: 'Area Control VO'). Virtual Outputs are programmed in the same way as Physical Outputs, except they only exist in the software (not the hardware). By convention, address Virtual Outputs to Output Expander 32, as per the image below.
  4. Create a Programmable Function which links the Virtual Output to the Area Group. This Programmable Function should be of type “Area Group Control”. It should have the Virtual Output as the Output you want to check, and specify the Area Group you created in step 2 (in the screenshot below, the function is controlling a group called 'All Areas').
  5. Set up a Virtual Input to control this Virtual Output. The Virtual Input will need an Area, and an Input Type – so create an Input Type (example name: 'Area Control Input Type'). In the General tab, set the Control Output to your Virtual Output. In the Options (1) tab, enable 'Generate Alarms' and 'Generate 24hr Alarms'. In the Options (2) tab, enable 'Toggle Control Output State On Alarm'.
  6. Create a Virtual Input (example name: 'Area Control VI'). As per Virtual Outputs, by convention assign Virtual Inputs to Input Expander 32. In the 'Areas and Input Types' tab, place the Virtual Input in the Automation Area and assign it the Input Type you created in step 5.
  7. Create a second Virtual Output (example name: 'Access Level VO'). Assign this to Output Expander 32.
  8. Create a Programmable Function that links the 'Access Level VO' output to the Virtual Input. This Programmable Function should be of type “Input Follows Output”. It should have the Virtual Input as the Input Follows Output, and the 'Access Level VO' as the output to check.
  9. Create an Access Level. In the General tab, set Time to Activate Output to 5 seconds, and enable 'Keypad Access Activates Output'. In the Outputs tab, add the Virtual Output created in step 7 (example name: 'Access Level VO').
  10. In Expanders|Keypads, go to the Options(1) tab and select 'Activate Access Level Output'. Do this for every Keypad from which you want users to be able to Arm/Disarm the Area Group in this way.
  11. Create a User, give them a PIN, and assign them the Access Level you created in step 9.
  12. Make sure your Automation Area is Armed.
  13. Finally, start both of the Programmable Functions you created. To do this, right-click on the Programmable Function and select Start.
Labels (1)
Labels:
  • EcoStruxure Security Expert
Tags (1)
  • Find more articles tagged with:
  • 19221
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore