Need to ensure that there are not any unresolved or invalid bindings
  • EcoStruxure Building Operation Workstation v1.5 and above
  • Bindings Diagnostics
Bindings are invalid because they point to something that cannot be bound together or they are unresolved because the binding points to an object that is not in the database.
From the Workstation run the Bindings Diagnostics to check for invalid or unresolved bindings.
  1. Open the Control Panel
  2. To Check the Status of Bindings  click the option for Bindings Diagnostics.
  3. Observe the Status to identify any invalid or unresolved bindings. Unresolved Binding.png
    Refer to the EBO Webhelp Binding Status Icons topic for more information
  4. Right-click the invalid or unresolved binding, edit the binding or view properties, and correct as appropriate. RightClickBinding.png