Unable to change set point from the thermostat when adjusting the value from a BAS
EcoStruxure Building Expert
Smart Struxure Lite
Misconfiguration of the object and BACnet priority level
1)     When discovering the object from the BMS, it will integrate as; type: numeric point | Property ID: Present value | Name: Occupied cool Setpoint as an example. The variable will be for reading only the actual value set.
2)     To change values from the BMS and thermostat, the object shall be configured as follow:
·        Type: numeric WRITEABLE
·        Enabled: True
·        Property ID: RELINQUISH DEFAULT
From the thermostat, If the value is highlighted in RED by going to set point page 1/2, the object is misconfigured repeat step 2