How to calibrate 102-AX airflow using the 102-AX LNS Plug-in or EBO TGML

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to calibrate 102-AX airflow using the 102-AX LNS Plug-in or EBO TGML
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Trey_Boothe
    Trey_Boothe
  • RobertAndriolo
    RobertAndriolo
  • RandyDavis
    RandyDavis
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
  • SESA128463
    SESA128463
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3275 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to calibrate 102-AX airflow using the 102-AX LNS Plug-in or EBO TGML

Picard Product_Support
‎2018-09-06 02:25 PM

Last Updated: Administrator CraigEl Administrator ‎2022-09-04 11:48 PM

Issue

Test and air balance procedure for balancing airflow

Product Line

TAC Vista, EcoStruxure Building Operation

Environment

  • Building Operation Automation Server Premium 
  • TAC Xenta 102-AX 
  • TAC Xenta 102-AX Plug-in

Cause

Each 102-AX controller must be calibrated on-site to report accurate airflow readings.  The LNS Plug-in provides this functionality, but it may not be immediately clear what the correct procedure is to perform a valid calibration.

Resolution

Check the firmware version of your 102-AX controllers in the plug-in, Node Configuration tab. It will be shown under Program Revision. If it's anything earlier than 2.1.6 then the calibration won't work properly. The airflow setpoint changes but the damper does not modulate to maintain setpoint in the calibration mode. Your options in that situation are to manually manipulate the damper to maintain airflow setpoint in order to facilitate calibration or upgrade the controllers firmware.

Also verify that the box is set to "Pressure Independent" mode on the Unit Parameters tab.  Pressure dependent boxes do not use airflow sensors, and therefore cannot be calibrated.

To balance the 102-AX in Building Operation version 1.4 or higher where the LNS plug-in is no longer provided, review the article TAC Xenta 102-AX TGML plug-in for Building Operation


To calibrate airflow using the 102-AX LNS plug-in: 

  1. Go to the Node Configuration Tab.
  2. Select "Set Default m & b." This is a good idea before each calibration attempt since incorrect calibration values can make it more difficult to perform a valid calibration.
    (NOTE: The m & b values can be viewed under the Airflow Parameters Tab of the 102AX LNS plug-in...m = Velocity Pressure Gain & b = Velocity Pressure Offset)
  3. Select "Start Calibration." At this point the airflow setpoint should go to the minimum. You can check the Cooling Minimum airflow setpoint on the Airflow Parameters tab.
  4. The damper now modulates to maintain the minimum cooling flow setpoint. Watch the VAV Reading (Low) and wait for it to hit the minimum flow setpoint and level out.
    If the airflow is fluctuating a lot, it could be that the low setpoint is below the threshold the box can confidently supply. Or it could be bad placement of the flow sensor in a turbulent area of the duct. It can affect your calibration greatly if the value is fluctuating too much.
    A relatively level reading will provide a good calibration.
  5. When it levels out, measure the actual airflow with a highly accurate magnehelic hood. Enter the actual value into Reference (Low) and select "Continue."
  6. The damper now modulates to maintain the maximum cooling flow setpoint. Watch the VAV Reading (High) and wait for it to hit the maximum flow setpoint and level out.
  7. When it levels out, measure the actual airflow with a highly accurate magnehelic hood. Enter the actual value into Reference (High) and select "Finish."
  8. The new calibrated m & b values are shown. The gain (m) is shown in the format of multiplier/divisor. Divide the values to get a decimal format of the gain. The closer to 1 this value is, the less calibration was required. actually gains of 2 or more indicate probable airflow reading problems. It may be advisable to reset factory calibration values and try the calibration again.
  9. The box should now be displaying values very close to actual measured readings. Test the low and high flow during normal operation using the Status Tab,
  10. Right click on the Space Temp and override the space temperature to a value equal to or greater than the Occupied Cooling Setpoint plus half the Cooling Band to drive the airflow setpoint to the cooling maximum airflow setpoint (you can find the Occupied Cooling Setpoint and Cooling Band on the Operating Tab). 
  11. With the space temperature already in override, left click the Space Temp to change the space temperature without taking it out of override, and set the space temperature to the Occupied Cooling Setpoint minus half the Cooling Band to drive the airflow setpoint to the cooling minimum airflow setpoint. 
  12. With the space temperature in override, right clicking it will take it out of override.
Labels (2)
Labels:
  • EcoStruxure Building Operation
  • TAC Vista
Tags (2)
  • Find more articles tagged with:
  • 4023
  • RobertAndriolo19
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore