Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

How does time sync function in AS-P react with BACnet MSTP devices?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How does time sync function in AS-P react with BACnet MSTP devices?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • Jeff
    Jeff
  • StephenYang
    StephenYang
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4134 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How does time sync function in AS-P react with BACnet MSTP devices?

Picard Product_Support
‎2018-09-10 06:31 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 07:12 PM

Issue

Customers question the time sync function in AS-P for BACnet devices

Environment

SE8650, Viconic, SBO, AS-P, SmartStruxure, Room Controller, MSTP, 3rd Party BACnet Devices

Cause

It is important to understand what happens when AS-P or Room Controller lose power.

Resolution

SE8650 firmware version 1.7.1-56d and SBO 1.9.3.24 were used in the test.

The testing was done with the fieldbus speed at both 38400 and 76800 baud.

1. The first test was to confirm AS-P sends out time sync signal 38 minutes after each hour periodically.
A review of all the timeSync data packets during the capture reveals that the time sync packets are sent every hour when the time in AS-P is 38 after the hour minutes mark.

image1-1.png

image1-2.png

image1-3.png
2. The second test was to confirm that the AS-P will send out a timeSync data packet if a device comes back online after a power outage.

First the time was synchronized between the SE8650 with AS-P.

image2-1.png

SE8650 was then powered down and the AS-P server time changed so that the times in the two devices would not match.

image2-2.png

 

A review of the time synchronization packets in the packet capture confirms that the AS sends out a time synchronization once the SE8650 is powered and boots up.

image2-3.png

3. If the AS-P and SE8650 both lost power the SE8650 will boot up before the AS-P. The AS-P will then sends out a timeSync once the BACnet communication is settled.

Labels (2)
Labels:
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
Tags (2)
  • Find more articles tagged with:
  • 19888
  • se8600
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.