Understanding Modbus Scattered Read Functionality

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Understanding Modbus Scattered Read Functionality
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Mahmoud_Sayed
    Mahmoud_Sayed
  • GavinHe
    GavinHe
  • sesa177673
    sesa177673
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3438 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Understanding Modbus Scattered Read Functionality

Picard Product_Support
‎2018-09-11 09:09 AM

Last Updated: Administrator CraigEl Administrator ‎2025-03-23 07:44 PM

Issue

Enabling Scattered read for Modbus device that doesn't support it can lead to poll fail, with Point Modbus Error: Illegal function code.

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Workstation (1.5 and above)
  • Building Operation Automation Server
  • Building Operation Automation Server Premium
  • Building Operation Automation Server Bundled
  • Building Operation Edge Server - Standard
  • Building Operation Enterprise Server

Cause

Requirement to optimize communication over Modbus to improve performance.

Resolution

The following is an extract from Web Help. The complete section can be viewed at  Modbus Batch Read Function:

 

'Scattered read is an enhancement to the batch read function that enables multiple, non-contiguous slave device registers to be read in a single Modbus query. By using the scattered read function, you can enable the Enterprise Server or Automation Server to avoid reading a large block of contiguous registers when it is only necessary to read a few registers. Also, using scattered read avoids the multiple use of group function codes 03 (analog output holding registers) and 04 (analog input registers) in order to read non-contiguous registers. Group function codes 01 (discrete output logic coils) and 02 (discrete input contacts) are not supported for scattered read.

 

Scattered read is available only for supported devices, for example, Schneider Electric branch circuit power meters with split core CTs. Furthermore, the scattered read function applies only when the Enterprise Server or Automation Server is operating as the client, not as a server. You can enable the scattered read function in the properties of all Modbus devices.

If a device does not support scattered read:

  • In V6 or higher: the polls will fail with an Illegal function code, so scattered read needs to be disabled if not supported by the Modbus device.
  • In V5 or below: the device is polled by the master device in the same way as if you had not enabled scattered read.'

 

The image below shows the properties dialogue window for a Modbus device and the corresponding setting.  The left is version 3.1 and above, the right is version 3.0 and below where it is referred to as 'Non-contiguous read'.  Refer to the Modbus TCP Device  section on Web Help for more information.

Scattered Read.png

  

 

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (4)
  • Find more articles tagged with:
  • 16886
  • GavinHeward22
  • MahmoudSayed25
  • PeterLarsen24
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now