Guidelines for creating Lonworks network in ES with L-IPs

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Guidelines for creating Lonworks network in ES with L-IPs
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • CraigEl
    CraigEl
  • sesa139513
    sesa139513
  • DavidFisher
    DavidFisher
  • Trey_Boothe
    Trey_Boothe
  • sesa115370
    sesa115370
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
2 Likes
3650 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Guidelines for creating Lonworks network in ES with L-IPs

Picard Product_Support
‎2018-09-11 04:58 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 06:53 PM

Issue

Additional information for creating Lonworks networks in ES, not covered by the StruxureWare Technical Guide.

Product Line

EcoStruxure Building Operation

Environment

StruxureWare Building Operation 1.3 SP1

Cause

Additional information for creating Lonworks networks in ES, not covered by the StruxureWare Technical Guide.

Resolution

Setup of the NIC852 network interface for the ES is covered in the StruxureWare Building Operation Technical Reference Guide, chapter 37.9

L-IP router setup is covered in the StruxureWare Building Operation Technical Reference Guide, chapter 37.10

 
Here are some additional points not covered in the Reference Guide:

To use the NIC852 as a network interface for the ES, you must configure the Loytec LConfig software to run as a service.  See Not able to get Service pin from LON devices connected with Loytec NIC from ES for more details.

The L-IPs must be used in Smart Switch mode in StruxureWare.  There are two Smart Switch modes:
1.  Smart Switch Mode
2.  Smart Switch mode with No Subnet Broadcast Flooding.
Only use the first of these modes.  This should be the default, out of the box.  See the L-IP User Manual for details of the DIP switch positions for each mode.

The ES version 1.3 can host up to 100 Xenta devices + 100 LON devices in total. These can be divided across 5 logical networks (different domains).
It is possible to have multiple L-IPs in the same network if needed - but the limit of 100+100 is per ES, not per network or L-IP.

Loytec recommend that in Smart Switch mode an IP channel should have no more than 10 L-IPs and packet rates no more than 500 packets/s.

If additional Xenta/LON devices are needed you can add them to one or more AS, below the ES.

Observe the standard Lonworks guidelines when creating your network topology e.g. maximum number of devices per network segment, maximum length of runs for the chosen cable type.  Group your devices so that network traffic across channels is minimized.

StruxureWare is unaware of your physical network topology - it just sees it as one big channel.  It will reserve a different subnet for each Xenta group you create, starting at subnet 253, but each Lonworks device you create will just be assigned the next available subnet/node address, starting at subnet 254 node 1.  This means that devices with the same subnet address will most likely appear on multiple physical channels.

The Loytec L-IP in Smart Switch Mode can still provide effective routing in this situation as it builds its routing table based on the physical location of subnet/node addresses, not just subnets.  Other manufacturers' routers, even in learning mode, may not be so forgiving.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • 13599
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore