Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Failure of Xenta Central Schedule after upgrading to 1.8.1

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Failure of Xenta Central Schedule after upgrading to 1.8.1
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Jonas_Brissman
    Jonas_Brissman
  • Product_Support
    Product_Support
  • RobertAndriolo
    RobertAndriolo
  • Benji
    Benji
  • PeterLarsen
    PeterLarsen

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1578 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Failure of Xenta Central Schedule after upgrading to 1.8.1

Picard Product_Support
‎2018-09-10 12:59 PM

Last Updated: Janeway Jonas_Brissman Janeway ‎2024-04-30 12:23 AM

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance.

Issue

When upgrading to 1.8.1 a Xenta Central Schedule that resides outside the LonWorks network it is not upgraded to the current version.

If the upgrade is attempted it breaks all the Xenta time schedule bindings with the Xenta Cental Schedule.

Product Line

EcoStruxure Building Operation

 

Environment

StruxureWare Building Operation 1.8.1

 

Cause

During the LonWorks Pre-upgrade only the objects under the LonWorks networks are upgraded.

If the Xenta Cental Schedule is located outside the LonWorks network this is not included in the upgrade process.

Resolution

Options to resolve this issue.

Before upgrading to 1.8.1

If the site uses Xenta Central Schedules, then use the server Hotfix 1.8.1.5101 to upgrade all the servers. Please contact Product Support and request Hotfix 1.8.1.5101.

After upgrade to 1.8.1

There are two options in this case:

  1. You can delete the Xenta Central Schedule and add a new Xenta Central Schedule. You are then able to bind the Xenta Schedules to the new Xenta Central Schedule.
     
  2. If there are many Xenta Schedules that refer to a Xenta Central Schedule you can use the export function to resolve the problem as shown here

Export the  Xenta Central Schedule as shown here

Once you have exported the Xenta Central Schedule you need to edit the exported XML file with Notepad++ and change the Xenta Central Schedule attributes from "lon" to "lon2". 

This is what the change should look like

Once this change has been made the XML File can be saved ready for an import to the Server.

Delete the existing Xenta Central Schedule from the database, making sure you check the box keep references.

Then import the edited XML to the server and this will re-establish the Xenta Central Schedule binding with the Xenta Schedules.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (3)
  • Find more articles tagged with:
  • 18913
  • defect32098
  • JonasBrissman24
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now