Issue
Editing a point on the MPM in Continuum via BACnet will result in the follwoing error message: "Communications failure due to routing device not available"
Product Line
Andover Continuum
Environment
SmartStruxure Lite Multi-Purpose Manager, Building Expert, CyberStation
Cause
Known Bug
Resolution
To resolve the issue, CyberStation must be updated.
Option 1:
Upgrade CyberStation to 2.0.
Option 2:
Download and apply the 921 hotfix to v1.94 SP1