Enhanced and Standard Alarm Delivery And getting out of mixed mode

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Enhanced and Standard Alarm Delivery And getting out of mixed mode
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • Alan_Wood
    Alan_Wood
  • Clifton_eakes
    Clifton_eakes
  • ScottLeedberg
    ScottLeedberg
  • DavidFisher
    DavidFisher
  • AdamSteele
    AdamSteele
  • sesa119747
    sesa119747
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2556 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Enhanced and Standard Alarm Delivery And getting out of mixed mode

Picard Product_Support
‎2018-09-06 02:52 PM

Last Updated: Admiral Alan_Wood Admiral ‎2022-11-04 01:48 PM

Issue

Enhanced and Standard Alarm Delivery Explained

Product Line

Andover Continuum

Environment

Cyberstation

Cause

Information on the difference between Enhanced Alarm Delivery and Standard Alarm Delivery feature.

Resolution

Standard Alarm Delivery:  
Prior to Continuum 1.7, alarms were delivered from the controller to each workstation on the network as long as a  Cyberstation is online (from the controller's perspective) AND if the Cyberstation is a recipient of the alarm or not.

 

The first workstation which receives the alarm logs it to the SQL database. The alarm is broadcast and if for some reason it doesn't get logged there is no guarantee it will be delivered to any Cyberstastion. It gets broadcast once.

 

Enhanced Alarm Delivery:
The alarm engine was changed so that alarms could be delivered to Workstations that were temporarily offline.

To accomplish this Continuum implemented Microsoft Message Queuing (MSMQ).

 

The controllers generate alarms based on criteria set up in alarm enrollments. These are logged in the database by the first workstation that receives the alarm which then hands it off to MSMQ for delivery to all workstations in the recipient list. The controller still sends the alarms to all online workstations. If a workstation is offline, alarms are stored in an outgoing MSMQ queue that will be delivered once the Cyberstation is back online.

 

Acc.App.AlarmServer.exe (Alarm Delivery Server) is the process that handles alarms and hands them off to MSMQ which is handled by the Windows Message Queuing service.

 

To view MSMQ queues, go to [Windows Control Panel>Security Settings]> Administrative Tools> Computer Management> Services and Applications> Message Queuing

 

Enabling Enhanced Alarm Delivery when upgrading or with a new install
This is accomplished by leaving the default checkbox for Enhanced Alarm Delivery selected in the database initialization step on a new install or when upgrading to a version greater than 1.7x. MSMQ will then be installed as part of the Cyberstation installation or upgrade.

 

Note: If the Enhanced Alarm Logging checkbox is not checked initially, the Enhanced Alarm Delivery checkbox may become unselectable. See Installing Continuum Database for the First Time on a Multi-User LAN System in the Installation Guide

 

Enabling enhanced alarm delivery in a system that doesn’t have the checkbox selectable

1. Manually Install MSMQ

    1. Start> Run> type cmd then click OK (to open a command prompt)
    2. At the DOS prompt type cd\ then enter (places the cursor at the root)
    3. cd \program files\continuum\install then enter
    4. Type cscript MSMQInstall.js then enter (Windows component wizard Installs MSMQ)
    5. When the script is finished, one of the lines will indicate that MSMQ started successfully
    6. Type exit

2. Updating the database

Note: Ensure you have a recent database backup before the next step

    1. Run Database Initialization
    2. Select Server if LAN or Stand Alone accordingly
    3. Select Enhanced Alarm Delivery checkbox
    4. Select update existing database and then click continue
    5. Restart all Cyberstations (If ALL aren't restarted, the system can still be in mixed mode)

 

3. LAN installation 

Manually install MSMQ on each Cyberstation according to the instructions above (step 1). MSMQ will now be used for guaranteed alarm delivery.

 

 

Caution:

Make sure that all Cyberststations in the database are restarted after Enhanced Alarm Delivery was selected and the DB Update performed! 

 

Not restarting a Cyberstation puts the system at risk of using workstations with both types of alarm delivery (PSS may refer to this as MIXED MODE).

 

If all but one of the Cyberstations gets restarted and a Continuum User changes the alarm delivery mode and then a Cyberstation gets restarted later, the system 

will be in mixed mode.

 

Uninstalling MSMQ

  1. Uninstalling MSMQ on a workstation (if needed at some point)
  2. Go to Control Panel> Add/Remove Windows Components> Deselect Message Queuing
  3. Say Yes to the warning message
  4. Reboot

Also, check the following:

  • Add a column to the alarm list view check the loggingWSId and see if the alarms are being delivered to another workstation that is no longer used. If it is no longer needed delete that Workstation which should correct this issue.
Labels (1)
Labels:
  • Andover Continuum
Tags (7)
  • Find more articles tagged with:
  • 2863
  • AlanWood22
  • alarms
  • CliftonEakes22
  • mixed mode
  • msmq
  • RobertAndriolo22
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore