EcoStruxure Building Operation object names limitation

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • EcoStruxure Building Operation object names limitation
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • Gary
    Gary
  • DavidFisher
    DavidFisher
  • RyanSuar
    RyanSuar
  • RobertAndriolo
    RobertAndriolo
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3456 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

EcoStruxure Building Operation object names limitation

Picard Product_Support
‎2018-09-06 11:44 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-22 07:56 PM

Issue

EcoStruxure Building Operation Automation Server, Enterprise Server and BACnet object names limitation

Dragging converted I/NET TGML graphics into Workstation causes Workstation to crash with following message:

Exception message: Object reference not set to an instance of an object.
System.NullReferenceException: Object reference not set to an instance of an object.
at SE.WorkStation.Base.Windows.Views.TgmlFileDropHandler.Drop(FileInfo, Path, IOperationContext, IProgressInfo)
at SE.WorkStation.Base.Windows.Views.FileDropCoordinator.ExecuteDrop(Path, IList`1, IProgressInfo)
at SE.WorkStation.Base.Windows.Views.<>c__DisplayClassd.b__9(IProgressInfo)
at SE.WorkStation.Framework.Services.<>c__DisplayClass1.b__0(IProgressInfo)
at SE.WorkStation.Framework.ProgressIndication.ProgressActionOperation`2.Run(IProgressOperationInternal, IProgressResult, IProgressOperationInfo)
at SE.WorkStation.Framework.Services.ProgressItem`1.b__1a(Task)
at System.Threading.Tasks.<>c__DisplayClasse`1.b__d()
at System.Threading.Tasks.Task`1.InvokeFuture(Object)
at System.Threading.Tasks.Task.InnerInvoke()
at System.Threading.Tasks.Task.Execute() 

Product Line

EcoStruxure Building Operation

Environment

Building Operation Workstation

Cause

The number of characters and the use of special characters in a EcoStruxure Building Operation object name and EcoStruxure Building Operation BACnet objects names

Resolution

Refer to the Webhelp Object Names topic for information on naming restrictions


The statements in Webhelp also apply to EcoStruxure Building Operation BACnet objects unless is it a Continuum b3 object. 

If you are creating a Continuum b3 object etc., the b3 object display name is limited to 16 characters consisting solely of letters, digits, and underscores (as per Continuum limitation).
Basically, any objects you create for Continuum, for example, a 'BACnet Analog Input (Continuum)' will be subjected to the Continuum limitation.

If you add a standard 'BACnet Analog Input' into an Automation Server or an Enterprise Server, then it is not limited by the Continuum limitation of 16 characters.


The most common issue when bringing I/NET TGML converted graphics into Workstation is not checking for spaces at either the beginning or end of the converted file name.  Make sure there are no spaces (white space) before or after any characters of the file name before copying into Workstation.


Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (13)
  • Find more articles tagged with:
  • 11143
  • asterisk
  • backslash
  • constraints
  • GaryMontague22
  • illegal
  • limits
  • mark
  • question
  • quotation
  • slash
  • supported
  • tilde
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore