Does SmartStruxure Lite support e-mail servers that require authentication?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Does SmartStruxure Lite support e-mail servers that require authentication?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • MaximeLaudren
    MaximeLaudren
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2533 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Does SmartStruxure Lite support e-mail servers that require authentication?

Picard Product_Support
‎2018-09-06 10:04 AM

Last Updated: Lieutenant MaximeLaudren Lieutenant ‎2022-08-18 09:04 AM

Issue

Unsure what options are available in the Lua smtp.send() function.

Product Line

EcoStruxure Building Expert

Environment

SmartStruxure Lite Multi-Purpose Manager (MPM)

Cause

The Lua smtp.send() function is not fully documented.

Resolution

The syntax of the smtp.send() function is:

smtp.send

{ from = string, rcpt = string or string-table, source = LTN12 source, [server = string,] [user = string,] [password = string,] [port = number,] [domain = string] }

 

From above you can see that the "from", "rcpt" and "source" fields are required. Whilst "server", "user", "password", "port" and "domain" fields are optional.

Example Lua code is:

--==============================================================================
-- SSL email notification script example
--==============================================================================

-- Define the input you want to monitor below
var("temperature", "ME.AI1") -- Room Temperature
limit = 78 -- define the threshold

now = scl.sysclock()
if (temperature > limit) then -- When temperature is above threshold
    if (sent == nil) -- Check if e-mail was already sent
    and ((last == nil) or (now - last > 15 * 60)) then -- Maximum every 15 minutes
        sent = true -- Only send e-mail once
        last = now -- Keep track of last time

    result, reason = smtp.send {
    user = "alerts@server.com",  -- Enter your existing SMTP username
    password = "test1234",  -- Enter your existing SMTP password
    from = "alerts@company.com",  -- Enter your existing Source address
    rcpt = {
            "user1@company.com",  -- First recipient
            "user2@company.com",  -- Second recipient
            "user3@company.com"  -- Third recipient
            },
    source = smtp.message( {
    headers = {
    from = "alerts@company.com",  -- Displayed source address
    to = "technicians@company.com",  -- Displayed recipients
    subject = "Temperature Alert"  -- E-mail title
                },
    body = "Current temperature is: " .. temperature .. " (above " .. limit .. ")" .. " [" .. os.date() .. "]"}),
    server = "server.com" – enter your SMTP server
                }

    if result ~= 1 then
        print(os.date(), "E-mail was NOT sent:", reason)
    else
        print(os.date(), "E-mail was successfully sent.")
    end
end
    else
    sent = nil -- Re-enable alerting on condition
end

 

--[[
Disclaimer: We hope that this script example and associated information (the
"information") is valuable to you. Your use of this information, however, is
at your sole risk. All information is provided "as -is", without any warranty,
whether express or implied, of its accuracy, completeness, fitness for a
particular purpose, title or non-infringement, and none of the third-party
products or information mentioned in the work are authored, recommended,
supported or guaranteed by Schneider Electric.. Further, Schneider Electric. shall
not be liable for any damages you may sustain by using/installing/modifying
this information, whether direct, indirect, special, incidental or
consequential, even if it has been advised of the possibility of such damages.
--]]



 

Labels (1)
Labels:
  • EcoStruxure Building Expert
Tags (2)
  • Find more articles tagged with:
  • 14382
  • MaximeLaudren22
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore