Differentiating Continuum LON IOU Modules. 485 vs FTT, Motorola vs Toshiba. Which file to use when upreving

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Differentiating Continuum LON IOU Modules. 485 vs FTT, Motorola vs Toshiba. Which file to use when upreving
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3191 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Differentiating Continuum LON IOU Modules. 485 vs FTT, Motorola vs Toshiba. Which file to use when upreving

Picard Product_Support
‎2018-09-11 01:12 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:38 AM

Issue

In the download center there are up to four files for the same version of the IOU modules firmware, how do I know which is the right file for my IOU module?

Product Line

Andover Continuum

Environment

Continuum IOU Module

Cause

The Neuron chip used in the Continuum IOU modules can support two different transceivers which are FTT-10A and RS-485, each type requires a different FW file.

Additionally, the IOU module originally used a Motorola Neuron Chip ***, in 2001 the Motorola Neuron chip had to be replaced with a Toshiba chip when Motorola ceased production of their Neuron chips. A 3rd chip was used after, the Cypress chip.

*** The AC-1 Plus, VT-1, Infistat, and LC-1 were not affected by the chip change as they did not use the Motorola Neuron chip. So you will only find 2 FW files for the same version and model these modules.

Resolution

1. When up revving Continuum IOU modules first determine if the module is FTT-10A or RS-485.

To determine the type lift the door cover of the IOU module and check the model written on the label. FT appended at the end of the model is for FTT-10A, RS-485 will either have 485 appended or only the model name with nothing appended at the end.

AC1PFTTAC1485.JPG

If the door cover is missing then remove the inner cover and take a look at the label on the chip itself. The picture below shows an AC1-Plus FTT-10A module indicated by the FT on the label.

AC1FTTChip.JPG

If the label is missing you can easily identify FTT versus 485 by removing the upper part of the enclosure and inspecting the components populated in the communication section of the circuit.

FTTVersus485_Hardware.jpg

On the Net Controller itself (99xx or 9680) there will be an ECHELON FT component similar to the one in the picture below located in the upper right corner of the board, the Net Controller's cover will need to be removed to see the component. 

FTTIdentifier.png

2. Verify which Neuron chip (Motorola or Toshiba) is installed in the IOU module.

IOUNeuronChip.JPG

3. Get the appropriate FW file from the download center.

IOUNeuronChipFourFiles.jpg

R&D had to recompile for the Toshiba chip.
The 20 version is the same as the 10 version and the 21 version is the same as the 11 version. Download the IO module firmware

Note: 
Version 10,11 are the Motorola processors 
Version 20 is the Toshiba processor 
Version 21 is the Cypress processor

Labels (1)
Labels:
  • Andover Continuum
Tags (4)
  • Find more articles tagged with:
  • 17398
  • AbeMeran20
  • AlanWood24
  • RandyDavis22
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore