Is it possible to convert a Xenta 121-HP to a Xenta 121-FC?
TAC Vista
Xenta 121
The hardware controller was purchased as a heat pump or fan coil unit, and the opposite is needed for the software application.
As of August 2011, it is possible.
  1. Download the NXE file and XIF file for the desired application
  2. Download the files to the Xenta 121 using Lonmaker or NL220
This will be blocked in the future.