Continuum version support for the CX9680/NC2 and the Conversion procedure from an NC1(99xx)

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Continuum version support for the CX9680/NC2 and the Conversion procedure from an NC1(99xx)
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Alan_Wood
    Alan_Wood
  • Dave_Shore
    Dave_Shore
  • JohnBoehmer
    JohnBoehmer
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2510 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Continuum version support for the CX9680/NC2 and the Conversion procedure from an NC1(99xx)

Picard Product_Support
‎2018-09-06 10:27 AM

Last Updated: Administrator CraigEl Administrator ‎2022-11-06 04:05 PM

Issue

Which Continuum versions support an NC2(9680)?
Procedure for replacing a CX99xx with a CX9680

Product Line

Andover Continuum

Environment

  • CX9940
  • CX9900
  • NetController 2 NCII CX9680

Cause

Netcontroller II (CX9680) is supported in Continuum versions 1.80 and higher

Resolution

Upgrade the site to Continuum 1.80 or higher for NC2 support

 

Procedure for converting an NetController1 (NC1/99xx) to a NetcontrollerII (NC2/9680)

To convert a NetController to a NetController II, perform the following steps:

 

    1. Back up your SQL Server database.
      See the Andover Continuum CyberStation Installation Guide, 30- 3001-720, and Microsoft® SQL server documentation.
    2. From the Continuum Explorer, use the right-click popup menu for this controller, and select Send to Text File.
      This drops the controller object’s data into a text file. For various ways to customize this operation, whereby you can save the controller’s child objects, please see the Send to Database Options in the CyberStation online help.
    3. Update your workstation with a version of CyberStation that supports the newer NetController models.
      These models are supported by CyberStation Version 1.8 and higher.
    4. Physically remove the old NetController, and mount/connect your NetController II.
      When you configure and commission the NetController II, use the same controller name, network IP address, and network ID. This is performed via the controller’s embedded web commissioning pages and via the General tab and the Network tab of the CyberStation’s Infinity Controller editor.
    5. Switch to CyberStation offline editing mode in the InfinityController editor.
    6. On the General tab, from the Controller Type dropdown menu, change the model number to 9680 or 9681, depending on which NetController II you are installing.
    7. Make sure you actually want to replace the NetController.
      When you attempt to change the controller model, Cyberstation displays a few warning messages:
      • Cyberstation warns that a model change is irreversible.
      • Cyberstation warns that, if an XDriver is used with this controller, not all XDrivers are supported by the new model.
      If you proceed, the XDriver links are left in place regardless of the availability of a replacement Xdriver.
      XDrivers on NetController II — In general, Xdrivers that are available on the bCX1 model 9640 are also supported on the NetController II.
      For example, supported NetController II XDrivers include, but are not limited to, the following:
      • Filter
      • XdTest
      • Modbus TCP
      • Modbus RTU

      XDrivers built for the previous-generation NetControllers will not run on the NetController II.


      What is an XDriver? An XDriver is special, customized software that your site purchases separately from TAC. The XDriver software allows your controller to connect to and communicate with a special piece of third-party equipment needed at your site. In the CyberStation CommPort editor, you must configure a controller comm port for this special device that the XDriver software enables.
      * When you leave the InfintyController editor, go back to online editing mode.
    8. If necessary, provide an updated XDriver file compatible with your NetController II. CyberStation prompts you to do this.
      Note: You can specify an XDriver on the General tab of the CommPort editor. Specify XDriver for the Default Mode, and use the browse button in the XDriver File Name field to search for and specify the path of the XDriver.
    9. Determine whether this NetController II has network security. If so, configure network security for this controller.
      Note: Network Security is supported only in NetController II model 9680, as well as ACX controllers 5720 and 5740.
    10. Restore (reload) data from your database into the new controller.
      From CyberStation’s Continuum Explorer, use the Object dropdown menu or right-click the object popup menu for this controller object, and select Send to Controller.
    11. Back up to flash. In Continuum Explorer, right-click over this controller, and from the container popup menu, select Backup to Flash.
      This saves the controller’s RAM configuration to its flash memory, in accordance with the attribute value that is set for the ACCRestartMode system variable.
Labels (1)
Labels:
  • Andover Continuum
Tags (7)
  • Find more articles tagged with:
  • 13087
  • 9680
  • AlanWood22
  • converting
  • DavidShore22
  • nc1
  • nc2
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of