Issue
Continuum reports an Unknown Model Number error.
Product Line
Andover Continuum
Environment
- Controller Model number
- Bootloader
- Learn
Cause
Possible reasons why Continuum may report an Unknown Model Number error.
- Controller is in bootloader mode.
- Controller is not responding fast enough due to a comm issue.
- The controller type saved in the Continuum database is different from the controller type physically installed.
- The total number of controllers exceeds the maximum number of nodes allowed on the Master.
- The baud rate of the bLink is not correctly set for the MSTP bus.
- The comm bus is not stable.
- Problems introduced to the bus due to a bad controller or electrical interference.
Resolution
- Communication issue must be troubleshot by using a combination of Controller error logs and LAN capture analysis.
- A controller can be brought out of bootloader mode by flashing the firmware.
- Create the device manually.
- Attempt to learn the controller onto the bus with no other controllers attached
- Correct misaligned baud rate settings.
- Run an ACCTrace at the Workstation during a learn to detect duplicate IDs.
Other articles that address this issue: