Continuum controller webpage displays incorrect values

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Continuum controller webpage displays incorrect values
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis
  • JohnBoehmer
    JohnBoehmer
  • JonGreen
    JonGreen

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1652 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Continuum controller webpage displays incorrect values

JohnBoehmer Schneider Alumni (Retired)
‎2021-10-27 08:03 AM

Last Updated: Picard RobertAndriolo Picard ‎2021-10-27 07:15 PM

Issue

Some of the fieldbus controller Output values presented on the Infinity controller's webpage do not agree with those values when viewed from Cyberstation and WebStation. 

Product Line

Andover Continuum

Environment

  • Continuum Cyberstation
  • Continuum webClient Server

Cause

Some controller outputs configuration are limited to specific output types. 

On the b3920 for example outputs 9 through 16 cannot be configured as digital outputs.

 

The ElecType (the outputs electrical type) stored in the Continuum database should match the output configuration in the controller's database.  But this is not always the case.  This can happen when the output configuration was imported from a text file.   

 

Controller output configuration viewed while the workstation is in Online mode

5 Online View - webpage out of sync.png

 

Controller output configuration viewed while the workstation is in Offline mode7 Offline Point type not right.png

 

 

When the controller webpage is displayed in a browser, the parent controller (cx9900, cx9680, bcx4040, bcx9640) makes a call for the point value to the fieldbus controller. 

If the ElecType for the output which is stored in the Continuum database is incompatible with the controller's output type, the parent controllers' call for the output value will fail.

Resolution

  1. Switch CyberStation to Offline mode
  2. Correct the outputs ElecValue to an appropriate type for the controller output
  3. Return CyberStation to Online mode
  4. Reload the fieldbus controller
Labels (1)
Labels:
  • Andover Continuum
Tags (4)
  • Find more articles tagged with:
  • controller webpage
  • htm
  • Infinity controller
  • JohnBoehmer21
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore