Considerations for Sigma System Controllers on Multiple VLANs

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Considerations for Sigma System Controllers on Multiple VLANs
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2318 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Considerations for Sigma System Controllers on Multiple VLANs

Picard Product_Support
‎2018-09-07 07:40 AM

Last Updated: Administrator CraigEl Administrator ‎2025-11-04 09:59 PM

Issue

Can Sigma system controllers sit on multiple VLANs?Can Sigma system controllers operate across multiple VLANs?

Product Line

Satchwell BAS & Sigma

Environment

Sigma UNC controllers

Cause

This is a common question raised by IT departments when planning to upgrade BAS systems to Sigma.

Resolution

Yes, Sigma controllers can be deployed across multiple VLANs. However, there are important considerations to ensure proper communication between devices:

1. Global Data Communication

  • Sigma global data is transmitted using the Ethernet broadcast address.
  • Most routers block broadcast messages between VLANs.
  • To enable global data exchange across VLANs, Link Addressing must be configured.

2. Link Addressing Requirements

  • Link Addressing acts as a tunneling mechanism to allow broadcast data to traverse VLAN routers.
  • A DNN (Data Network Node) must be added to each sub-LAN to support Link Addressing.
  • For detailed configuration steps, refer to Link Addressing on a Sigma System

3. Default Gateway Configuration

All Sigma devices must be configured with appropriate default gateway IP addresses:

  • Controllers:
    Use the Pocket Terminal command:

    GW + 192.168.0.1
    

    (Replace 192.168.0.1 with the actual default gateway of the local network.)

  • DNNs:
    Set a Static Route as defined in the article:
    "Having set Link Addressing in a Sigma DNN3 can no longer communicate..."

  • Sigma Servers:
    Set the default gateway via:
    Network Settings > Internet Protocol (TCP/IP) > Properties


Recommendation

While Sigma controllers can operate across VLANs, a flat VLAN architecture is generally simpler to configure and maintain. Use multiple VLANs only when necessary and ensure all Link Addressing and gateway configurations are correctly implemented.

Labels (1)
Labels:
  • Satchwell BAS & Sigma
Attachments
Tags (2)
  • Find more articles tagged with:
  • 4761
  • CraigEllis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore