Having set Link Addressing in a Sigma DNN3 can no longer communicate to the DNN3 and Link Addressing does not work.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Having set Link Addressing in a Sigma DNN3 can no longer communicate to the DNN3 and Link Addressing does not work.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1864 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Having set Link Addressing in a Sigma DNN3 can no longer communicate to the DNN3 and Link Addressing does not work.

Picard Product_Support
‎2018-09-06 02:19 PM

Last Updated: Administrator CraigEl Administrator ‎2025-10-07 06:57 PM

Issue

After configuring Link Addressing on a Sigma DNN3, communication with the DNN3 fails, and Link Addressing does not function as expected.

Product Line

Satchwell BAS & Sigma

Environment

  • Multiple Sigma controllers across at least two Ethernet VLANs
  • DNN3 devices (version 1.h) connected to each VLAN
  • Port 1 of each DNN3 connects to the VLAN
  • Port 2 is configured as a virtual Serial PPP port (not physically connected to a device)

Cause

Although Link Addressing may be correctly configured, the DNN3 devices lack routing information (i.e., static routes).
Without this, the DNN3 cannot transmit point-to-point global data to the appropriate router or default gateway.

Additionally:

  • With both ports configured, RIP (Routing Information Protocol) is enabled by default.
  • RIP broadcasts misleading routing information, advertising port 2 as a valid route, which is incorrect.
  • RIP must be disabled to prevent this false advertisement.

Resolution

To restore communication and proper Link Addressing functionality:

  1. Add a default static route to each DNN3 using Pocket Terminal 32 via the service port:

    SR+ 0.0.0.0/0 192.168.1.253 1
    
    • 0.0.0.0/0 is the generic destination and mask
    • 192.168.1.253 is the default gateway
    • 1 is the DNN3 port number
  1. Disable RIP on port 1 of the DNN3:

    RIPD 1
    

Additional Notes

  • Ensure that no devices are physically connected to port 2 if it's configured as a virtual PPP port.
  • This configuration ensures that global data is routed correctly between VLANs and prevents routing conflicts.
Labels (1)
Labels:
  • Satchwell BAS & Sigma
Tags (2)
  • Find more articles tagged with:
  • 4258
  • CraigEllis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore