Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Link Addressing on a Sigma System

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Link Addressing on a Sigma System
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • DavidChild
    DavidChild
  • sesa125819
    sesa125819
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2622 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Link Addressing on a Sigma System

Picard Product_Support
‎2018-09-07 06:14 AM

Last Updated: Administrator CraigEl Administrator ‎2025-11-04 08:42 PM

Issue

When Sigma operates over a site-wide Ethernet network with multiple subnets—or when Sigma DNNs use ARCnet or Ethernet secondary LANs—global object values may not be received by controllers located on different subnets. This results in communication failures between controllers.

Product Line

Satchwell BAS & Sigma

Environment

Sigma Ethernet networks containing subnets.

Cause

Global values are broadcast messages that are not routed across third-party Ethernet routers. Without proper configuration, these messages are blocked, preventing communication between controllers on different subnets.

Resolution

To enable global data transmission across subnets, Link Addressing (LA) must be configured. This process encapsulates broadcast messages into IP packets, allowing them to traverse routers and reach the intended devices.

Refer to PIB 05.01.05-3 – Rules for Using Link Addressing for full technical guidance.

📎 Attachment: PIB050105_3 Link Addressing.pdf


Key Concepts

What is Link Addressing?

  • Sigma uses broadcast messages for global data exchange.
  • Routers block these broadcasts to prevent network flooding.
  • Link Addressing converts broadcasts into directed IP packets.

Firmware Requirements

  • Ensure controllers and DNNs are running firmware version 5s (controllers) and 5t (DNNs) or later.
  • Earlier versions may not support Link Addressing reliably.

Configuration Commands (via Pocket Terminal)

  • LA+ <IP> — Add a Link Address
  • LA- <IP> — Remove a Link Address
  • LAD — Display all Link Addresses
  • LAC — Clear all Link Addresses

⚠️ Maximum of 5 Link Addresses per device
⚠️ On older firmware, Link Addresses may be deleted when downloading the CO??.SET file


Examples of Link Addressing Scenarios

1. Basic Two-Subnet Configuration

  • Node 10: LA+ 10.44.101.20
  • Node 20: LA+ 10.44.100.10
  • Required for bidirectional global data exchange.

2. DNNs Bridging Subnets

  • Node 100 (DNN): LA+ 10.44.101.20
  • Node 101 (DNN): LA+ 10.44.100.10
  • DNNs rebroadcast global messages to their subLANs.

3. Multi-Subnet Circular Configuration

  • Treat the network as a circle.
  • Link Addressing should be configured clockwise and anti-clockwise, but avoid loops unless using advanced group configurations.

4. Using DNNs for Re-Broadcasting

  • Add DNNs to subnets with multiple controllers.
  • Only DNNs need Link Addresses; they rebroadcast to all local controllers.

Advanced Configuration

Global Message Lifetime

  • Each global message starts with a Life Time Count of 15.
  • Each DNN hop decrements the count.
  • Messages are discarded when the count reaches 0.

Large Networks (15+ Subnets)

  • Use grouped DNNs with “Daisy Chain” Link Addressing.
  • Interconnect groups with selected DNNs to form a resilient ring.

Monitoring and Maintenance

  • Use Sigma Device Monitoring to ensure DNNs are operational.
  • Monitor for DNN failures which can disrupt global data flow.

DNN Configuration for Re-Broadcasting

  • Configure DNN as a router using Port 2.
  • Add a new serial network in Sigma System Manager.
  • No physical connection is needed on Port 2.

Best Practices

  • Avoid loops unless using grouped DNNs.
  • Limit global traffic to prevent network performance issues.
  • Use DNNs to simplify Link Addressing in complex subnet environments.
Labels (1)
Labels:
  • Satchwell BAS & Sigma
Attachments
Tags (4)
  • Find more articles tagged with:
  • 4613
  • CraigEllis25
  • DavidChild19
  • DavidChild20
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore