Configuring Security Expert Reporting Service such as Contact ID

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Configuring Security Expert Reporting Service such as Contact ID
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • AdamSteele
    AdamSteele
  • David_Kendrick
    David_Kendrick

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2083 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Configuring Security Expert Reporting Service such as Contact ID

Guinan AdamSteele Guinan
‎2021-03-12 02:46 AM

Last Updated: Admiral David_Kendrick Admiral ‎2023-04-04 08:45 AM

Issue

Instructions are required, on how to set up and troubleshoot a Contact ID Reporting Service.

Product Line

EcoStruxure Security Expert

Environment

  • Security Expert Client
  • SP-C-WEB
  • Contact ID Reporting Service

Cause

Basic information on configuring reporting services is documented in the Security Expert Operator Manual and SP-C-WEB Programming Reference but these do not contain practical steps on configuring this specifically for Contact ID reporting.

Resolution

The Contact ID Service is used to send Alarms, Tests, and Events using Contact ID reporting to a 3rd Party monitoring station capable of receiving the Contact ID format.

 

The following steps can be used to configure a basic setup of Contact ID.

Note that a modem will be required and modem events can be logged in the events window for troubleshooting.

 

1. Go to Programming | Phone Numbers. Add your phone numbers, usually primary and backup.

ReportIDx1.png

 

2. Go to Programming | Services. Add a new service, set Service Type to ContactID.

Set Service Mode to 1 - Start With controller OS.

ReportIDx2.png

3. Set the Client code and select the previously created phone number

ReportIDx3.png

4. Select required report options.

Log Modem Events to Event Buffer option will log all events. Only use this for troubleshooting.

ReportIDx4.png

 

5. Go to Programming | Areas and assign the Service to required Areas

ReportID2.png

6. Go back to Programming | Services.  Right-click the Service record, and select Start Service.

  • Without doing this the service will not be running.
  • It needs to be manually started the first time.
  • Check the controller Health Status to see the status of your service if it is started or stopped.

ReportIDx5.png

When done configuring your Services, Inputs, and Areas. Select Reports | Central Station Report.

  • Select the Reporting Service and the output directory to generate the file.
  • Click Generate and a CSV and HTML file will be generated.ReportIDx6.png
  • This report can be provided to the central station for their database.
  • The HTML version is the easiest to read.

 

Further details on the Contact ID reporting format and outlines of the reporting and mapping options can be found in the AN 316 Security Expert - Contact ID Reporting in Security Expert and SP-CWEB - Integration Guide application note.

 

For Details of creating Test Reports for Reporting Services see KB Article :

Creating a Trouble Input for Periodic Testing of a Reporting Service such as Contact ID

Labels (1)
Labels:
  • EcoStruxure Security Expert
Tags (2)
  • Find more articles tagged with:
  • AdamSteele21
  • DavidKendrick23
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore