Creating a Trouble Input for Periodic Testing of a Reporting Service such as Contact ID

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Creating a Trouble Input for Periodic Testing of a Reporting Service such as Contact ID
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • David_Kendrick
    David_Kendrick
  • AdamSteele
    AdamSteele

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1939 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Creating a Trouble Input for Periodic Testing of a Reporting Service such as Contact ID

Admiral David_Kendrick Admiral
‎2023-04-04 08:43 AM

Last Updated: Guinan AdamSteele Guinan ‎2023-04-20 11:52 PM

Issue

Instructions are required on how to set up a Trouble Input for Periodic Testing of a Reporting Service such as Contact ID

Product Line

EcoStruxure Security Expert

Environment

  • Security Expert Client/Server
  • SP-C-WEB
  • Contact ID Reporting Service

Cause

Basic information on configuring reporting services is documented in the Security Expert Operator Manual and SP-C-WEB Programming Reference but these do not contain practical steps on configuring Trouble Inputs for Period Testing of Reports Services such as Contact ID

Resolution 

Trouble Input:

1. Navigate to Programming | Trouble Inputs

2. Locate the Service Test Report Trouble Input

3. Select the Areas and Input Type Tab

4. Select an Area and Input Type that the Trouble Input will be processed by

ReportID1.png

Area

Generally all trouble inputs that need to be monitored by a central station are monitored by the same area referred to as a system Area. This Area generally does not have any output such as Sirens associated with it, does not process intrusion inputs and is not accessible by end users.  A system Area is not created by default in Security Expert so needs to be added via the Programming | Areas menu

 

Input Type 

Generally the default Input Type of Trouble Silent of 24 Hour Alarm is used for Trouble Inputs

5. Select Save

6. Navigate to Programming | Areas and select the System Area 

7. Select the Configuration Tab and ensure the Reporting Service eg ContactID is assigned to the Area.ReportID2.png

8. Save

 

Periodic Testing:

1. Navigate to Sites | Controllers

2. Change Test Report Time (HH:MM) to specified time period, the Service Test Report Trouble Input will open at this frequency eg. every 4 hours and report to the station if there is a connection between the panel and the monitoring station.ReportID3.png

3. Select the Options Tab

4. Select Test Report Time is periodic tick boxReportID4.png

5. Save

For more details on the creation of Report Services such as Contact ID please refer to KB Article:  Configuring Security Expert Reporting Service such as Contact ID

Labels (1)
Labels:
  • EcoStruxure Security Expert
Tags (1)
  • Find more articles tagged with:
  • DavidKendrick23
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore