Best practices when commissioning ZigBee networks

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Best practices when commissioning ZigBee networks
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • SaidSawan
    SaidSawan
  • CraigEl
    CraigEl
  • Cody_Failinger
    Cody_Failinger

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
5101 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Best practices when commissioning ZigBee networks

Picard Product_Support
‎2018-09-11 08:22 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-10 09:36 PM

Issue

Controllers may leave their network and join another if a nearby network has an identical "Extended network ID", "Channel" or "PAN ID"

Product Line

EcoStruxure Building Expert

Environment

  • SmartStruxure Lite Multi-Purpose Manager
  • SE8xxx Room controller
  • SE8000 Series
  • SER8300, SE8300, SE8350
  • Ex. Viconics branding VT8000 Series

Cause

Conflict in zigbee networks (Same "Channel", same "PAN ID" or Same "Extended Network ID")

Resolution

Before deployment, and in order to ensure having a reliable ZigBee network, one has to be aware of the best practices and the limitations of RF signals. Here are some key points to be considered

Network Conflicts: Always change your Extended Network ID from the factory default. The best thing is to use a naming convention that makes sense. One suggestion would be to use "SSLLITxx," where "xx" is replaced by the floor the network is on. For example, floor 5 would be "SSLLIT05." If you have multiple networks on the same floor, adding a letter code helps denote them. For example, if there were 2 networks on floor 5, "SSLLI05A" and "SSLLI05B" can be used.

1.png

Note: In Firmware 2.20.1, the ZigBee Extended Network ID parameter is set by default to a unique string based on the serial number of the MPM. This will eliminate the possibility of having duplicate Extended ID's in a new deployment. For existing installations, the Extended Network ID will remain unchanged if upgrading from a previous version.

 

Alternating Channels: Alternating channels between network will minimize interference ensure stability. For example, for a 5-story building, alternate between channels 20, 25, 20, 25, 20.

2.jpg

Tx Power Upgrade: The default value for "Tx Power" is 5dBm which was designed in order to meet various regulations in certain countries (Europe). However, the "Tx Power" can be increased to 18dBm in other regions of the world (North America) to boost the transmission power of the MPM.

3.png

 

Interference: There are different types of interference when a wireless signal travels through a given space:

  • Physical objects: The number of walls the wireless signal can pass through is determined by the density of the materials used in a building's construction. Concrete and steel walls are difficult for a signal to pass through. These structures will weaken or at times completely prevent wireless signals.

Also, the presence of individuals or water will diminish the signal due to the water's ability to absorb the signal.

  • 2.4Ghz Frequency Interference:
    • Cordless Phone - operates on the same frequency as the ZigBee and can cause a significant decrease in performance.
    • Microwave Oven - operates by emitting a very high power signal in the 2.4GHz band. Often emits a very "dirty" signal across the entire 2.4GHz band.
    • Wireless Routers - Wireless Wi-Fi Networks that share the same channel will have a negative effect on ZigBee network performance.
  • Distance: To ensure reliable communications, a suitable distance between two devices has to be calculated before installation. The distance depends on three factors; transmitter power, sensitivity of the receiver and the propagation path loss. The latter is dependent on the number of walls/physical objects obstructing the signal.
  • Locations: The physical location where a router or coordinator is placed also has an impact on the signal. Place the devices in higher ground to reduce the impact of physical objects.


Route Redundancy: It is critical that the signal has multiple routes to hop from one device to the other, from one edge of the network to the opposite edge. (See example in images below)

4.png

5.png

Labels (1)
Labels:
  • EcoStruxure Building Expert
Tags (3)
  • Find more articles tagged with:
  • 17877
  • mpm-un-014-5045
  • working
Was this article helpful? Yes No
100% helpful (3/3)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore