Backup of EcoStruxure Building Operation AS and ES

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Backup of EcoStruxure Building Operation AS and ES
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Hernan_Urueña
    Hernan_Urueña

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
14666 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Backup of EcoStruxure Building Operation AS and ES

Picard Product_Support
‎2018-09-10 07:08 AM

Last Updated: Administrator CraigEl Administrator ‎2025-11-13 03:44 PM

Issue

Steps to backup within EcoStruxure Building Operation (EBO)

Product Line

EcoStruxure Building Operation

Environment

EcoStruxure Building Operation site with AS and/or ES

Backup, Automation Server, Enterprise Server, Workstation, .xbk, xbk, backup set, db backup, db_backup

Cause

Must an AS or ES be stopped in order to do a full backup? Is a raw copy of the database folder from within Windows Explorer sufficient for backing up an ES? 

For instructions on how to restore a backup in StruxureWare/EcoStruxure Building Operation, see How to restore a EBO server backup set.

Resolution

  • No need to stop AS or ES: EBO freezes the database during backup.
  • Configuration changes are queued until backup completes; historical data is buffered.
  • Do not use raw folder copy: Always use the built-in backup function.
  • Three rules to remember:
    1. Restores must use the same software revision.
    2. Do not rename the backup set.
    3. If renaming is needed, zip the backup and rename the zip file.

Default backup schedule: Every Sunday at 1:00 AM.

  • When creating a backup, give the appropriate prefix to the standard name format. See screenshot below.

    Hernan_Uruea_0-1762925736467.png

  • The backup file will be shown as the screenshot below.

    Hernan_Uruea_1-1762925787994.png

  • Should the backup name need to be changed, then either create a new backup, or zip up the backup using the new name.

Backup Procedure

Enterprise Server (ES) Automation Server (AS)

  1. In Workstation, select the Server in the System Tree.
  2. Go to Actions → Backup.
  3. In Backup Options:
    • Include column: Select servers to include.
    • Backup content:
      • All Data: Historical + configuration databases.
      • Configuration only: Configuration database only.
    • Add a Backup set description (up to 255 characters).
  4. Click Backup.
  5. Verify that each backup succeeded and click Close.

Backup file location:
C:\ProgramData\Schneider Electric\StruxureWare\Building Operation 1.X\Enterprise Server\db_backup\LocalBackup
or
C:\ProgramData\Schneider Electric\EcoStruxure\Building Operation 2.X\Enterprise Server\db_backup\LocalBackup

 
Backup Files of AS:

  • Log in to AS from Workstation.
  • Navigate to System → Backup and Restore → Backup sets → Local.
  • Right-click the backup file → Save To... (choose folder on HDD).
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (4)
  • Find more articles tagged with:
  • 7313
  • HernanUruena23
  • HernanUruena24
  • HernanUruena25
Was this article helpful? Yes No
100% helpful (4/4)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore