Attempts to change Controllers IP address fails and unable to reset to default IP address

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Attempts to change Controllers IP address fails and unable to reset to default IP address
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • Product_Support
    Product_Support
  • AdamSteele
    AdamSteele
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1780 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Attempts to change Controllers IP address fails and unable to reset to default IP address

Picard Product_Support
‎2018-09-10 02:31 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 06:29 PM

Issue

Controllers IP address needs to be changed but any attempt to do so results in the IP address reverting back to what it was previously configured for.

Product Line

Andover Continuum

Environment

  • Continuum
  • CX9702
  • BCX controllers
  • NC2 controllers
  • ACX57xx controllers

Cause

The Controller has hit the Flash writes circuit breaker and is no longer able to save any changes to Flash. This includes updating Device settings such as IP address and ACC Node ID. The controller error log may also contain an error similar to below when attempting to make any such changes.

 

10/08/2014 19:00:22.00 0x00004406         0x03b76100        0x0004cb68         0x003e2000        0x000007d1

                                        DEVICE_ERR_ERASE_LIMIT      (Flash circuit breaker tripped. CX97XX code base)

Resolution

One of the two methods to reset the Flash circuit breaker listed below should then allow the controller to write to Flash again.

 

1. accstatusbackup = accbackupenable
 
For more information see Caution when using PE programs to perform an automatic flash backup on a controller.
 
 
2. INFFlashDisabled.
 
Create a numeric in the controller with the following name and alias:
 
INFFlashDisabled
 
A value  greater than 0 usually indicates that the flash circuit breaker had tripped, though in some cases you may find these errors occurring when INFFlashDisabled = 0. In either case, once the value of this numeric is set to 0 and applied,  the flash circuit breaker errors should stop.
Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 18298
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of