Issue
The alarm bell icon, which should appear on Pinpoint door controls when the door is in an alarm state, is not visible.
Product Line
Andover Continuum
Environment
Pinpoint graphics interface
Cause
The door control is positioned on a lower graphic layer, and the alarm icon is being obscured by another graphic component placed above it.Resolution
To resolve the issue:
- Select the affected door control in the Pinpoint interface.
- Right-click on the door control.
- Choose "Bring to Front" from the context menu.
This action ensures the door control (and its associated alarm icon) is rendered above other graphic elements.
Additional Notes:
- This issue is purely visual and does not affect the underlying alarm functionality.
- Consider reviewing graphic layer arrangements when designing or modifying Pinpoint views to prevent similar issues.