Adding an object to an already opened Trend chart does not work correctly in Webstation
  • Adding an object to an already opened Trend chart does not work correctly in Webstation
  • sesa139513
    sesa139513
  • CraigEl
    CraigEl
  • sesa125819
    sesa125819
‎2018-09-11 06:14 AM
Last Updated: Administrator CraigEl Administrator ‎2022-08-09 08:40 PM
Adding an object to an already opened Trend chart does not work correctly.
  • Webstation
  • Open chart
  • Adding objects
An AS or ES is logged into using a Webstation, and an existing Trend chart is opened. An object is then selected in the System Tree, and then using the right-hand menu, the "Open Chart" and "Add to already open chart" is selected. Values are not added to the already opened chart.
This issue is caused by a Java 7 update 51 a specific fix is not available.
Possible workarounds;
  • Use an earlier version of Java.
  • Change Java security level to Medium.
  • Add site to the exception list
For further details on "adding to the exception list", refer to Webstation graphics not working after Java updated to Java 7 update 51.
Tags (2)
  • 15539
  • PeterLarsen24