Dear Community Members, We are currently experiencing a technical issue that is affecting the ability to create new posts. Our team is actively investigating the root cause and working to resolve it as quickly as possible. We apologize for the inconvenience and appreciate your patience. SE Community Team!
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Link copied. Please paste this link to share this article on your social media post.
Hi
Please can anyone assist in how to scale a modbus analog point ? On workstation
Thank you
Link copied. Please paste this link to share this article on your social media post.
You need to look at the Gain property of the Modbus point
Gain is the multiplication factor you can apply to the value to be read from or written to a register. For example, a multiplication factor of 0.5 causes the return of a value that is half of the value stored in an addressed register. Similarly, a multiplication factor of 2 causes the return of a value that is twice the value stored in the register. For example, the datasheet for a meter states that a certain register contains a voltage value in mV. The value returned is 243087, but you may prefer to see this value as 243.087 V, so you apply a Gain of 0.001.
Link copied. Please paste this link to share this article on your social media post.
You need to look at the Gain property of the Modbus point
Gain is the multiplication factor you can apply to the value to be read from or written to a register. For example, a multiplication factor of 0.5 causes the return of a value that is half of the value stored in an addressed register. Similarly, a multiplication factor of 2 causes the return of a value that is twice the value stored in the register. For example, the datasheet for a meter states that a certain register contains a voltage value in mV. The value returned is 243087, but you may prefer to see this value as 243.087 V, so you apply a Gain of 0.001.
Link copied. Please paste this link to share this article on your social media post.
Hi Craig
Thank you for the assistance , and my problem is solved now.