Which is right for my customer? MGE 30kVA or VT Smart-UPS 30kVA

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

Solved
AlexLindsay_apc
Cadet
0 Likes
1
245

Which is right for my customer? MGE 30kVA or VT Smart-UPS 30kVA

This was originally posted on APC forums on 5/23/2012


We are really new to including UPSs as part of our solutions. I am familiar with APC products from our smaller scale applications but have never worked with equipment of this size.

I notice a difference in suggested retail price but do not see much difference between the MGE Smart Online or the APC Smart-UPS. Could someone please highlight the major differences I should consider and perhaps which one, from your experience, is the best solution for a customer?


Accepted Solutions
upsguy_apc
Commander
Commander
0 Likes
0
245

Re: Which is right for my customer? MGE 30kVA or VT Smart-UPS 30kVA

This was originally posted on APC forums on 5/24/2012


The APC MGE Galaxy 3500 and the APC SUVT are very similar, the main difference is the MGE unit has a different NEMA rated enclosure and a built in air filter.

See Answer In Context

1 Reply 1
upsguy_apc
Commander
Commander
0 Likes
0
246

Re: Which is right for my customer? MGE 30kVA or VT Smart-UPS 30kVA

This was originally posted on APC forums on 5/24/2012


The APC MGE Galaxy 3500 and the APC SUVT are very similar, the main difference is the MGE unit has a different NEMA rated enclosure and a built in air filter.