Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Where to find UPS model and serial number with PCSS

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Where to find UPS model and serial number with PCSS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2151
Teken
Teken
156
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
LarryK
LarryK
Mentor

Posted: ‎2024-06-10 08:29 AM

0 Likes
3
3552
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-10 08:29 AM

Where to find UPS model and serial number with PCSS

Using PCPE, you could go to the following registry entry, HKEY_LOCAL_MACHINE\SOFTWARE\WOW6432Node\APC\PowerChute Personal Edition\3.1.0, select the TechnicalData node and obtain the model number and serial number of the device being monitored by the software.

 

Knowing that, I was able to create scripts to help maintain data in Excel about my fleet.

 

Can anyone tell me where PCSS keeps this same information, because I cannot find it?

 

Thanks!

Labels
  • Labels:
  • Home & Office - UPS & Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
LarryK
LarryK
Mentor

Posted: ‎2024-12-13 11:42 AM . Last Modified: ‎2024-12-17 10:57 AM

In response to LarryK
1 Like
0
3195
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-13 11:42 AM . Last Modified: ‎2024-12-17 10:57 AM

Using the latest ChatGPT 4.o model, I have refined @BillP original code snippet:

 

# GetAPCDeviceInfo
#
# Obtain device Model and Serial number from the APC PCSS log
#
$computername = $env:computername
Write-Output "Current System '$computername'"

$location = "C:\Program Files\APC\PowerChute Serial Shutdown\agent\log\pcss.log"
$search4 = "Device detected!!"

# Read the log file and find the last line containing "Device detected!!"
$lastDetectedLine = Get-Content $location |
Where-Object { $_ -match $search4 } |
Select-Object -Last 1

# Regex pattern to capture the model number after "model:" and remove any trailing comma or spaces
$modelPattern = 'model:\s*([^,]+)' # This will capture the model number up to the first comma or space

# Regex pattern to capture the serial number after "serial num:" and remove any trailing comma or spaces
$serialPattern = 'serial num:\s*([^,]+)' # This will capture the serial number up to the first comma or space

# Check if the lastDetectedLine matches the model pattern
if ($lastDetectedLine -match $modelPattern) {
$modelNumber = $matches[1] # Extracted model number
Write-Output "The model number is: $modelNumber"
} else {
Write-Output "Model number not found."
}

# Check if the lastDetectedLine matches the serial pattern
if ($lastDetectedLine -match $serialPattern) {
$serialNumber = $matches[1] # Extracted serial number
Write-Output "The serial number is: $serialNumber"
} else {
Write-Output "Serial number not found."
}

Hope that helps someone!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
BillP Leader
Leader

Posted: ‎2024-06-12 05:25 AM

1 Like
2
3515
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-12 05:25 AM

@LarryK 

 

You can query the pcss.log file for the information using PowerShell.

 

Run the command 

Select-String -Path C:"\Program Files\APC\PowerChute Serial Shutdown\agent\log\pcss.log" -pattern 'Back-UPS' (The command is entered assuming PowerChute has been installed to the default path.)

BillP_0-1718194508256.png

You will also find the information in the About.

BillP_1-1718194706092.png

 

Reply

Link copied. Please paste this link to share this article on your social media post.

LarryK
LarryK
Mentor

Posted: ‎2024-06-12 11:34 AM

In response to BillP
0 Likes
1
3503
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-12 11:34 AM

@BillP - This sample is significant help.  Of course I'm going to have to change all of my existing scripts, but...


I'm going to suggest that the -pattern value should be 'Device detected!!' because not everyone will be using a Back-UPS device.

 

Also, I changed your sample to the following:

 

$location = "C:\Program Files\APC\PowerChute Serial Shutdown\agent\log\pcss.log"
$search4 = "Device detected!!"

Get-Content $location |
Where-Object { $_ -match $search4 } |
Select-Object -Last 1

This will get the last entry in the log file with the most current serial number.

Reply

Link copied. Please paste this link to share this article on your social media post.

LarryK
LarryK
Mentor

Posted: ‎2024-12-13 11:42 AM . Last Modified: ‎2024-12-17 10:57 AM

In response to LarryK
1 Like
0
3195
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-13 11:42 AM . Last Modified: ‎2024-12-17 10:57 AM

Using the latest ChatGPT 4.o model, I have refined @BillP original code snippet:

 

# GetAPCDeviceInfo
#
# Obtain device Model and Serial number from the APC PCSS log
#
$computername = $env:computername
Write-Output "Current System '$computername'"

$location = "C:\Program Files\APC\PowerChute Serial Shutdown\agent\log\pcss.log"
$search4 = "Device detected!!"

# Read the log file and find the last line containing "Device detected!!"
$lastDetectedLine = Get-Content $location |
Where-Object { $_ -match $search4 } |
Select-Object -Last 1

# Regex pattern to capture the model number after "model:" and remove any trailing comma or spaces
$modelPattern = 'model:\s*([^,]+)' # This will capture the model number up to the first comma or space

# Regex pattern to capture the serial number after "serial num:" and remove any trailing comma or spaces
$serialPattern = 'serial num:\s*([^,]+)' # This will capture the serial number up to the first comma or space

# Check if the lastDetectedLine matches the model pattern
if ($lastDetectedLine -match $modelPattern) {
$modelNumber = $matches[1] # Extracted model number
Write-Output "The model number is: $modelNumber"
} else {
Write-Output "Model number not found."
}

# Check if the lastDetectedLine matches the serial pattern
if ($lastDetectedLine -match $serialPattern) {
$serialNumber = $matches[1] # Extracted serial number
Write-Output "The serial number is: $serialNumber"
} else {
Write-Output "Serial number not found."
}

Hope that helps someone!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore