SmartUPS C1000 code L.01 on display

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • SmartUPS C1000 code L.01 on display
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
Start a Topic
MikeInMA
MikeInMA
Cadet

Posted: β€Ž2023-02-01 06:55 AM

0 Likes
10
10258
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2023-02-01 06:55 AM

SmartUPS C1000 code L.01 on display

I have a SmartUPS C1000 that is displaying code L.01 on the front panel - the UPS seems to be working normally otherwise.  What does this code mean - I cannot find reference to it in the owners manual or in my online searches.

 

Thanks

Labels
  • Labels:
  • Home & Office - UPS & Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 10
DSJones15
DSJones15
Cadet

Posted: β€Ž2023-10-05 08:49 AM

0 Likes
1
8069
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2023-10-05 08:49 AM

The owner's manual says the meaning of this code is "LifeTimeNearEnd". What I don't know is, does this refer to the batteries or the unit as a whole.

Reply

Link copied. Please paste this link to share this article on your social media post.

manu67a
manu67a
Cadet

Posted: β€Ž2023-11-25 03:02 AM

In response to DSJones15
0 Likes
0
7574
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2023-11-25 03:02 AM

This refers to the battery

Reply

Link copied. Please paste this link to share this article on your social media post.

fuff8135
fuff8135
Cadet

Posted: β€Ž2024-05-07 01:44 PM

0 Likes
0
6353
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2024-05-07 01:44 PM

I have replaced the battery and the code is still there. Is there anyway to reset unit after battery has been changed?

 

Reply

Link copied. Please paste this link to share this article on your social media post.

lwbrown
lwbrown
Cadet

Posted: β€Ž2024-12-12 11:31 AM

0 Likes
1
4259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2024-12-12 11:31 AM

I need to know how to reset the L.01 also

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: β€Ž2024-12-13 12:04 PM

In response to lwbrown
0 Likes
0
4230
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2024-12-13 12:04 PM

Please refer to this resource link. Page 11 indicates how to enter the Configuration Mode. Page 13 explains how to update the system when the battery has been replaced:

 

https://download.schneider-electric.com/files?p_enDocType=User+guide&p_File_Name=SU_UM_990-5444E_MN0...

 

Questions Ask - If not and this answered your query please mark this reply as a solution. As it will help the next person asking the same. πŸ‘

Reply

Link copied. Please paste this link to share this article on your social media post.

nlovering
nlovering
Cadet

Posted: β€Ž2025-11-17 04:41 AM

0 Likes
4
612
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2025-11-17 04:41 AM

I reset the rb1 variable and rebooted the unit.  I briefly saw the full battery status, but the unit returned to the L.01 code displayed.  What can be the issue?  Thx.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: β€Ž2025-11-18 05:01 AM

In response to nlovering
0 Likes
3
597
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2025-11-18 05:01 AM

Did you actually replace the RBC or just attempted to clear the active error?!? If the RBC was not replaced than you can use this APC FAQ to mute the error:

 

https://www.se.com/us/en/faqs/FAQ000260345/

If the RBC is indeed EOL it must be replaced as changing RB1 flag will have no impact (IF) the RBC continues to fail the weekly Self Test! ☝️

 

Questions Ask . . . πŸ‘

Reply

Link copied. Please paste this link to share this article on your social media post.

nlovering
nlovering
Cadet

Posted: β€Ž2025-11-20 03:35 PM

In response to Teken
0 Likes
0
531
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2025-11-20 03:35 PM

Yes, I did replace the battery.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

nlovering
nlovering
Cadet

Posted: β€Ž2025-11-20 03:36 PM

In response to Teken
0 Likes
1
531
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2025-11-20 03:36 PM

The message continues to appear with the new battery.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: β€Ž2025-11-21 02:09 AM

In response to nlovering
0 Likes
0
520
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2025-11-21 02:09 AM

You may consider performing the Brain Dead Reset and report back the results:

 

https://www.se.com/ca/en/faqs/FA156611/

 

As an aside please confirm via Power Chute software the battery installation date if available. If present use the application to change and update the same.

 

Question's Ask . . . πŸ‘ 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore