Smart-UPS X 3000 does not charge from ecoflow

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Smart-UPS X 3000 does not charge from ecoflow
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Janeway Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
UkraineUser
Crewman UkraineUser
Crewman

Posted: ‎2024-12-04 08:48 AM

0 Likes
10
793
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-04 08:48 AM

Smart-UPS X 3000 does not charge from ecoflow

I want to increase the battery life of my equipment. I already have an extra battery for 3000, plus I bought an Ecoflow Delta2 max. The UPS is constantly clattering and doesn't want to charge. Do you have any ideas? In Ukraine, it is actual.

Labels
  • Labels:
  • Home & Office - UPS & Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Teken
Janeway Teken
Janeway

Posted: ‎2024-12-13 06:23 AM . Last Modified: ‎2024-12-13 06:25 AM

In response to UkraineUser
0 Likes
0
573
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-13 06:23 AM . Last Modified: ‎2024-12-13 06:25 AM

Appreciate you providing all of the logs and screen captures. It’s quite apparent the power being generated by the eco flow is less than ideal as such the UPS is reacting poorly.

 

I am very reluctant to suggest the following given the unit is no longer in warranty, this upgrade process may result in a completely bricked system. ☹️


Since you’re at war this would leave you with no UPS hardware. 

Regardless, please read the latest firmware release notes for v15 which I have appended here:

 

https://download.schneider-electric.com/files?p_Doc_Ref=Smart-UPS_FW_Release_Notes&p_File_Name=SMX10...

 

Your system is currently at 7.4 and 8.1 offers a few important fixes and enhancements in how the system operates when input voltage is poor.

 

More specifically items fixed / resolved in action items: 1, 7, 8, 9, 10.

 

The latest UPS firmware will bring that hardware to v15.0 which includes v8.1 fixes as listed up above.

 

Below is the link to download the latest FUW (Firmware Update Wizard) which will automatically detect the (correct firmware) and install the same onto the target UPS:

 

https://www.apc.com/us/en/faqs/FA279197/

 

I have also appended an APC forum thread which I call out what must be done and in place:

 

https://community.se.com/t5/APC-UPS-Data-Center-Enterprise/APC-UPS-SMX1500-firmware-update-failure-a...

 

NOTE: I can not stress enough updating any APC UPS firmware is extremely dangerous and can lead to a bricked / broken system! Please consider this before doing so as there is no guarantee this will resolve the issues you see now. 

But, the action items listed up above have solved many problems related to power input quality for many. The firmware must be loaded using only the supplied proprietary APC RJ50 -> RS232 Serial cable or one you bought and validated to work or one you made.

 

Do (NOT) attempt to upload the firmware through the NMC / USB! NMC must be removed during this process.

 

Questions Ask . . . 👍

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
Teken
Janeway Teken
Janeway

Posted: ‎2024-12-04 10:40 PM

0 Likes
0
792
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-04 10:40 PM

Upload the data & event logs from the system for review if there is a NMC. If no NMC (Network Management Card).

 

You can record the information from the LCD / Logs. You can also retrieve some logs from the APC Power Chute Software if the UPS is connected to a computer running the above (PCBE / PCSS) software. 

Slava Ukraine . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

UkraineUser
Crewman UkraineUser
Crewman

Posted: ‎2024-12-05 12:12 AM

0 Likes
0
757
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-05 12:12 AM

This one log?

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

UkraineUser
Crewman UkraineUser
Crewman

Posted: ‎2024-12-05 01:31 AM

0 Likes
7
751
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-05 01:31 AM

Data log. At 10:54:36 we connect Ecoflow. After some time UPS was Shutdown on 11:00:36, probably because the relay couldn't switch for more than a certain amount of time

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Janeway Teken
Janeway

Posted: ‎2024-12-05 04:55 AM

In response to UkraineUser
0 Likes
6
733
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-05 04:55 AM

You may consider adjusting the following settings to see how the system behaves and reacts:

 

Local Power / Power Quality: Change this from good to either two options of (Fair / Poor). This defines when the system will go into battery only mode.

 

Transfer Voltage: Adjust the upper & lower input transfer voltage. This setting defines when the AVR circuit will engage.

 

Sensitivity: Adjust from normal to either (reduced / low). This defines when the system will go into battery only mode.

 

Let me know how the new settings affect the system from operating and if it allows charging from the eco flow. 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

UkraineUser
Crewman UkraineUser
Crewman

Posted: ‎2024-12-06 12:59 AM . Last Modified: ‎2024-12-10 11:30 PM

In response to Teken
0 Likes
0
697
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-06 12:59 AM . Last Modified: ‎2024-12-10 11:30 PM

In the process of testing above, at the moment of sudden shutdown of the UPS we had a server and 1 switch down. Therefore, we will pause and not test for the time being....

Update

Found out why it shut down, the error--

1 12/05/2024 11:00:33.427 135 Backfeed Relay Hardware Fault

Reply

Link copied. Please paste this link to share this article on your social media post.

UkraineUser
Crewman UkraineUser
Crewman

Posted: ‎2024-12-10 11:29 PM

In response to Teken
0 Likes
4
612
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-10 11:29 PM

Tested, changed Sensitivity parameter in the process, it doesn't work. Transfer Voltage is in a wide range and Power Quality is not found in our APC.....

12/10/2024 19:02:46 209.02 211.41 209.08 2.06 13.52 14.41 49.98 99.00 136.47 +22.46 19.0 18.0 40.0
12/10/2024 19:01:46 0.00 236.52 210.91 2.03 13.49 14.36 49.98 99.00 136.47 +22.42 19.0 18.0 41.0
12/10/2024 19:00:46 210.52 211.56 211.05 2.03 13.48 14.38 50.00 99.03 136.50 +22.49 19.0 18.0 41.0
12/10/2024 18:59:46 209.06 211.95 211.42 2.03 13.50 14.44 50.00 99.02 136.47 +22.48 19.0 18.0 42.0
12/10/2024 18:58:46 0.00 233.23 211.11 2.03 13.48 14.39 50.00 99.01 136.47 +22.48 19.0 18.0 43.0
12/10/2024 18:48:46 208.34 214.06 212.97 2.00 13.35 14.36 50.00 100.00 130.75 +22.55 19.0 18.0 46.0
12/10/2024 18:38:45 205.47 213.38 212.48 2.00 13.34 14.32 50.00 100.00 130.75 +22.55 19.0 18.0 46.0
12/10/2024 18:28:45 206.39 211.25 210.80 2.03 13.45 14.39 50.00 100.00 130.75 +22.56 19.0 18.0 45.0
12/10/2024 18:18:45 202.27 211.20 210.02 2.03 13.36 14.31 50.00 100.00 130.75 +22.58 19.0 18.0 43.0

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Janeway Teken
Janeway

Posted: ‎2024-12-12 01:56 AM

In response to UkraineUser
0 Likes
3
593
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-12 01:56 AM

Can you provide a link to the specific model Eco Flow Max you have on hand that provides the technical specifications?!?

 

Please also upload the data, event, and UPS Fault logs from the NMC here. Along with a screen capture of the UPS power options and their setting.

 

Lastly, please call out what UPS / NMC firmware is installed and the serial number of the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

UkraineUser
Crewman UkraineUser
Crewman

Posted: ‎2024-12-13 04:57 AM

In response to Teken
0 Likes
2
576
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-13 04:57 AM

https://eu.ecoflow.com/products/delta-2-max-portable-power-station

firmwares versions in txt files.

Model
Smart-UPS X 3000
SKU
SMX3000HVNC
Serial Number
AS1839256029
Firmware Revision
UPS 07.4 (ID1003)
Manufacture Date
09/30/2018

 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Janeway Teken
Janeway

Posted: ‎2024-12-13 06:23 AM . Last Modified: ‎2024-12-13 06:25 AM

In response to UkraineUser
0 Likes
0
574
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-13 06:23 AM . Last Modified: ‎2024-12-13 06:25 AM

Appreciate you providing all of the logs and screen captures. It’s quite apparent the power being generated by the eco flow is less than ideal as such the UPS is reacting poorly.

 

I am very reluctant to suggest the following given the unit is no longer in warranty, this upgrade process may result in a completely bricked system. ☹️


Since you’re at war this would leave you with no UPS hardware. 

Regardless, please read the latest firmware release notes for v15 which I have appended here:

 

https://download.schneider-electric.com/files?p_Doc_Ref=Smart-UPS_FW_Release_Notes&p_File_Name=SMX10...

 

Your system is currently at 7.4 and 8.1 offers a few important fixes and enhancements in how the system operates when input voltage is poor.

 

More specifically items fixed / resolved in action items: 1, 7, 8, 9, 10.

 

The latest UPS firmware will bring that hardware to v15.0 which includes v8.1 fixes as listed up above.

 

Below is the link to download the latest FUW (Firmware Update Wizard) which will automatically detect the (correct firmware) and install the same onto the target UPS:

 

https://www.apc.com/us/en/faqs/FA279197/

 

I have also appended an APC forum thread which I call out what must be done and in place:

 

https://community.se.com/t5/APC-UPS-Data-Center-Enterprise/APC-UPS-SMX1500-firmware-update-failure-a...

 

NOTE: I can not stress enough updating any APC UPS firmware is extremely dangerous and can lead to a bricked / broken system! Please consider this before doing so as there is no guarantee this will resolve the issues you see now. 

But, the action items listed up above have solved many problems related to power input quality for many. The firmware must be loaded using only the supplied proprietary APC RJ50 -> RS232 Serial cable or one you bought and validated to work or one you made.

 

Do (NOT) attempt to upload the firmware through the NMC / USB! NMC must be removed during this process.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Janeway Teken
Janeway

Posted: ‎2024-12-13 07:45 AM

In response to UkraineUser
0 Likes
0
557
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-13 07:45 AM

As an aside if you have not considered the following items this may be a possible solution / option.

 

Inverter: Purchase a 12 volt pure sine wave inverter that can be connected to the Eco Flow. Than attach the UPS to the inverter which should offer a cleaner output in terms of voltage / frequency such as this example:

 

https://a.co/d/gGyQ9BQ

 

Keep in mind the link is offering an example of the hardware and not a recommendation of buying this specific brand etc. You’ll obviously purchase the correct hardware for your regions voltage and frequency and power handling.

 

AVR: You may purchase an AVR with the appropriate power handling which essentially is a transformer with various output voltage taps. The key feature of any high quality AVR is it maintains and regulates the output voltage and frequency like your APC UPS. 

Transformer: You may consider buying a 1:1 isolation transformer. This device isolates the input from output and provides a regulated voltage / current / frequency.

 

UPS: You may consider buying another used (simple) pure sine wave UPS. The older APC SAU, SURT models were more tolerant to dirty power. The unit doesn’t need to have any batteries as you’re just using it as a big filter so the SMX3000 can recharge its cells / stay online instead of going into battery only mode. 

 

All of the above are possible options for you given your current situation. I did not suggest any of these as this obviously requires spending finances and having the ability to purchase the same.

 

Just throwing out some ideas . . . 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of