Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
What RCD (GFCI) for SRT3000RMXLi and SUA3000RMI? (if any)
APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-08-1305:24 AM
What RCD (GFCI) for SRT3000RMXLi and SUA3000RMI? (if any)
I have a small server room at home, and the whole building is protected by a standard household 30 mA RCD breaker.
Everything worked fine when I was only using an SUA3000RMI, but after adding an SRT3000RMXLi, the RCD trips whenever the UPS switches to battery power.
What’s the best approach here? Should I bypass the RCD for the server room, or bypass the main RCD and install a dedicated one for it? If so, what type of RCD should be used, especially for the SRT3000RMXLi?
The only RCD-related information I’ve found is for a much larger 250–400 kVA UPS, which recommended using a Type B RCD — but those are quite expensive.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-08-1404:27 AM. Last Modified: 2025-08-1404:28 AM
I would ask you to validate this problem by doing the following:
SRT: Remove this unit from the mains outlet and power down.
SUA: Leave this unit in place and report back the behaviour. If nothing happens during the next power fluctuation disconnect this unit from the mains power and shut it down.
SRT: Connect and power up the system and report back what you observe. During this test only the UPS is connected with (No) loads to mains power.
If nothing happens during the next power fluctuation connect the same loads as before. Report back what you observe and if the GFCI breaker trips choose any random load and remove until the GFCI stops tripping.
If the GFCI breaker trips regardless of any connected load removed one at a time until none are present.
Provide the following logs when the system goes into battery only mode: Event, Data, UPS
Regardless of the above you have some options to consider and try in no specific order of relevance:
Power Quality: Decrease the sensitivity from normal to low and report back the results. This setting defines when the unit will go into battery only mode.
Transfer Voltage: Adjust both high and low transfer voltage to a wider range. This setting defines when the unit goes into AVR mode in Line Interactive systems.
On the SRT this defines when the bypass is available and used as a mains source.
Frequency / Slew: Adjust both to a wider range and report back the results and behaviour.
All of the above costs you nothing but time and effort.
Should none of the above work than the following action items may be required or considered:
If the unit is still under APC Warranty submit a RMA and see if the problem is solved. If the new unit behaves the same than your options are these:
GFCI Breaker: Replace with a different make / model.
Bypass: Provide dedicated power from a standard breaker from the service panel and install a GFCI outlet (IF) available.
If a GFCI outlet is not available than use a GFCI power bar to mimic the same. Insure the power bar is short as possible and has the same or better wire diameter.
Given the SRT is a 30 amp unit it’s highly unlikely you’ll find a outlet. So the 220 - 240 VAC GFCI power bar is the only option.
This last option circumvents the GFCI Breaker using a standard breaker. Using a GFCI power bar connected to the UPS outlets provides GFCI protection (IF) required and needed.