UTS6H: One Circuit trips when going from Gen Power back to Utility Power

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • UTS6H: One Circuit trips when going from Gen Power back to Utility Power
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
100
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:01 PM . Last Modified: ‎2024-03-21 04:00 AM

0 Likes
6
1003
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:01 PM . Last Modified: ‎2024-03-21 04:00 AM

UTS6H: One Circuit trips when going from Gen Power back to Utility Power

Hi, I've got a UTS6H being powered by a Honda EU2000i. I had my first outage last week, and everything worked great. (Still have some learning to do related to load shedding). However, my issue is that whenever I got from Generator power back to Utility Power (whether when testing or with a real power outage), one circuit breaks. It's the Circuit to the kid's bedrooms. Which is the one circuit that I don't want to break. It's not a huge deal, I just have to go down and reset the circuit, but has anyone come across this and found a solution? The Kid's bedroom circuit also powers the home theater. But, when I test, everything in the home theater is off. Feel free to ask questions about the setup if that can get me to a resolution.

Labels
  • Labels:
  • Universal Transfer Switch
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:01 PM . Last Modified: ‎2024-03-21 04:00 AM

0 Likes
0
1003
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:01 PM . Last Modified: ‎2024-03-21 04:00 AM

Thanks Angela, I'll try a new breaker and report back.

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:01 PM . Last Modified: ‎2024-03-21 04:00 AM

0 Likes
0
1003
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:01 PM . Last Modified: ‎2024-03-21 04:00 AM

What type of breaker is it that is tripping in the panel? 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:01 PM . Last Modified: ‎2024-03-21 04:00 AM

0 Likes
0
1001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:01 PM . Last Modified: ‎2024-03-21 04:00 AM

it's just a 15 amp circuit. Set to Lights on the UTS.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:01 PM . Last Modified: ‎2024-03-21 04:00 AM

0 Likes
0
1003
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:01 PM . Last Modified: ‎2024-03-21 04:00 AM

But what about the breaker? What type is it - a standard breaker or something like AFCI/GFCI?

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:01 PM . Last Modified: ‎2024-03-21 04:00 AM

0 Likes
0
1003
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:01 PM . Last Modified: ‎2024-03-21 04:00 AM

It's a standard breaker. Though I may need to do a double check if the bathroom GFCIs are on this breaker. I didn't think they were. In fact, I have another breaker labeled by the builder as Bath GFI.

 

Thanks Angela.

 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:01 PM . Last Modified: ‎2024-03-21 04:00 AM

0 Likes
0
1003
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:01 PM . Last Modified: ‎2024-03-21 04:00 AM

Hi Rudy,

I chatted with my colleague who knows a lot more about these things than I do. He said he could only think that the circuit was actually becoming overloaded. (We asked on the AFCI/GFCI because the UTS won't work well with those). The breaker could be too sensitive, though, I imagine you have other circuits with this same one/type. Breakers aren't also super-duper accurate either so do you think you could be close to overloading this circuit by chance? And also, frequent trips may have resulted in a weak connection since they are typically meant for tripping once and replacing.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:01 PM . Last Modified: ‎2024-03-21 04:00 AM

0 Likes
0
1004
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:01 PM . Last Modified: ‎2024-03-21 04:00 AM

Thanks Angela, I'll try a new breaker and report back.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of