APC UTS10BI + HONDA EM4500SX + APC Smart-UPS 3000 RM X whit 240 Volt IN/OUT question

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • APC UTS10BI + HONDA EM4500SX + APC Smart-UPS 3000 RM X whit 240 Volt IN/OUT question
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
119
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:01 PM . Last Modified: ‎2024-03-21 04:00 AM

0 Likes
1
620
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:01 PM . Last Modified: ‎2024-03-21 04:00 AM

APC UTS10BI + HONDA EM4500SX + APC Smart-UPS 3000 RM X whit 240 Volt IN/OUT question

Hello,
I recently purchased a new UTS10BI for work with a Honda EM4500SX generator whit remote control kit.
Sorry for my bad english 😞
I have a very good UPS model Smart-UPS 3000 RM X 240 Volt model.
I need that when power outages from watt hour meter for a long time the universal transfer switch automatically turns on the generator and do not download all the batteries of the UPS.
I have connect the wire 9 IN and 10 IN to my 240 Volt in watt hour meter but the UTS10BI not power on,only i hear a relay close,no leds and no disply switch on.
To be able to turn and see the operating uts I have purchased a 240 volt transformer primary 240 Volt and secondary 120 Volts 300 VA and I plugged the cable into the UPS Inlet.
Please can you help me, I spent a lot of money, time and no one knows how to help me to connect these devices.
I already called two professionals but they do not know the UTS10BI.

Many thanks!

Mauro

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:01 PM . Last Modified: ‎2024-03-21 04:00 AM

0 Likes
0
620
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:01 PM . Last Modified: ‎2024-03-21 04:00 AM

Hi Mauro, 

Your profile indicates you are in Italy - is that still accurate? UTS10BI is designed for North America use with 2 phases @ 240V (so H-H-G) and 60Hz. If you're still in Italy feeding this one single leg of 230V or 240V @ 50Hz which is what we'd expect in Europe, it won't work. In North America, this needs to be installed by a licensed electrician and they should know what to check for the input power connection.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:01 PM . Last Modified: ‎2024-03-21 04:00 AM

0 Likes
0
621
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:01 PM . Last Modified: ‎2024-03-21 04:00 AM

Hi Mauro, 

Your profile indicates you are in Italy - is that still accurate? UTS10BI is designed for North America use with 2 phases @ 240V (so H-H-G) and 60Hz. If you're still in Italy feeding this one single leg of 230V or 240V @ 50Hz which is what we'd expect in Europe, it won't work. In North America, this needs to be installed by a licensed electrician and they should know what to check for the input power connection.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore