Posted: 2021-06-29 06:01 PM . Last Modified: 2024-03-21 04:00 AM
Hi, I've got a UTS6H being powered by a Honda EU2000i. I had my first outage last week, and everything worked great. (Still have some learning to do related to load shedding). However, my issue is that whenever I got from Generator power back to Utility Power (whether when testing or with a real power outage), one circuit breaks. It's the Circuit to the kid's bedrooms. Which is the one circuit that I don't want to break. It's not a huge deal, I just have to go down and reset the circuit, but has anyone come across this and found a solution? The Kid's bedroom circuit also powers the home theater. But, when I test, everything in the home theater is off. Feel free to ask questions about the setup if that can get me to a resolution.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:01 PM . Last Modified: 2024-03-21 04:00 AM
Thanks Angela, I'll try a new breaker and report back.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:01 PM . Last Modified: 2024-03-21 04:00 AM
What type of breaker is it that is tripping in the panel?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:01 PM . Last Modified: 2024-03-21 04:00 AM
it's just a 15 amp circuit. Set to Lights on the UTS.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:01 PM . Last Modified: 2024-03-21 04:00 AM
But what about the breaker? What type is it - a standard breaker or something like AFCI/GFCI?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:01 PM . Last Modified: 2024-03-21 04:00 AM
It's a standard breaker. Though I may need to do a double check if the bathroom GFCIs are on this breaker. I didn't think they were. In fact, I have another breaker labeled by the builder as Bath GFI.
Thanks Angela.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:01 PM . Last Modified: 2024-03-21 04:00 AM
Hi Rudy,
I chatted with my colleague who knows a lot more about these things than I do. He said he could only think that the circuit was actually becoming overloaded. (We asked on the AFCI/GFCI because the UTS won't work well with those). The breaker could be too sensitive, though, I imagine you have other circuits with this same one/type. Breakers aren't also super-duper accurate either so do you think you could be close to overloading this circuit by chance? And also, frequent trips may have resulted in a weak connection since they are typically meant for tripping once and replacing.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:01 PM . Last Modified: 2024-03-21 04:00 AM
Thanks Angela, I'll try a new breaker and report back.
Link copied. Please paste this link to share this article on your social media post.