Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

UTS10BI gives CKT fault condition - CKT8 No output.

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: UTS10BI gives CKT fault condition - CKT8 No output.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2151
Teken
Teken
156
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 12:07 AM . Last Modified: ‎2024-03-20 12:24 AM

0 Likes
14
3265
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:07 AM . Last Modified: ‎2024-03-20 12:24 AM

UTS10BI gives CKT fault condition - CKT8 No output.

UTS10BI gives CKT fault condition - CKT8 No output.   Does this just mean the fuse is blown?  I recently moved the unit from one house to another so I'm wondering too if I should just reset to factory default as well to clear any previous settings that may not align but as soon as  I applied power and gave it time to do its initial diagnostic it came up with the error posted above and said reset or call tech support.

  Any ideas??   The manual doesn't give this specific "not output" that I saw when reading through the troubleshooting.

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
BillP Leader
Leader

Posted: ‎2021-06-30 12:08 AM . Last Modified: ‎2024-03-20 12:23 AM

0 Likes
0
3265
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:08 AM . Last Modified: ‎2024-03-20 12:23 AM

I don't think it is a setting, especially since you reset it to defaults. I checked on my end with to see if there was anything you missed and at this point, we don't see what else it could be beyond the breakers, wires, fuse, etc. We're thinking an RMA may be in order unfortunately undecided

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 14
BillP
BillP Leader
Leader

Posted: ‎2021-06-30 12:07 AM . Last Modified: ‎2024-03-20 12:24 AM

0 Likes
0
3265
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:07 AM . Last Modified: ‎2024-03-20 12:24 AM

Hello,

I found that when you see No Output, it means "A circuit no output fault happens when the unit detects there is no output voltage present when the source voltage it is powered from is good."

Yes, we should check the fuse but it can also be the breaker on the panel for this circuit. If neither of those check out, the only other thing we can think of is that a faston fell off somewhere. If you check the fuse and breaker, then I don't know if you can provide a picture of the inside so we could see if we can tell (if you don't see anything obvious).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 12:07 AM . Last Modified: ‎2024-03-20 12:24 AM

0 Likes
0
3265
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:07 AM . Last Modified: ‎2024-03-20 12:24 AM

Great thanks!   So the no output could occur if the wires came apart from the breaker or inside the UTS10 and thus the no output voltage...  I currently have all breakers in the off position in the main breaker panel b/c this is a new construction and I don't have all the wires completely landed so I didn't want the power to go out but it sounds like this is just testing from the UTS10 output so maybe a faston inside the UTS10 came loose.   I'll take a look and post a picture if I can't find anything.  Thank you very much for the help.   I need to figure this out before the HVAC guy shows up next week as the 9/10 runs the minisplit!   I'm pretty excited I finally found a useful output for a 240/20 amp breaker smile  I can heat and cool even when the power is down.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-30 12:07 AM . Last Modified: ‎2024-03-20 12:24 AM

0 Likes
0
3265
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:07 AM . Last Modified: ‎2024-03-20 12:24 AM

Sounds awesome! Hope you find something obvious and it is a quick fix. cool

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 12:07 AM . Last Modified: ‎2024-03-20 12:24 AM

0 Likes
0
3265
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:07 AM . Last Modified: ‎2024-03-20 12:24 AM

so....   I checked the connections and they all seemed tight.  reset the unit and got the same error.   I replaced the fuse and got the same error.   I then reset to factory default and after it reset I got a CKT fault for 7 and no output now.   The number 8 light actually went off and now all the other circuit lights are blinking (previously 8 was blinking with all the other circuits).  I'm guessing that means 8 isn't working at all.  Circuit 9/10 are solid red lights which I believe just means it is getting power.  So I'm guessing all the circuits will give me the same error which means there is no output from the unit on any circuit???  bummer.  Should I try to call the technical support number and see if there is a step by step?   Should I go buy new fuses for all the circuits? 

I do have one question which I kind of feel like I mentioned but didn't emphasis...  does having the breaker off at the panel cause this error?   It says output but does it really mean input.   Will this error occur if the breaker is off and cause the circuits to say no output and blink?   Is this what happens when there is a power failure?

Jeff

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-30 12:07 AM . Last Modified: ‎2024-03-20 12:23 AM

0 Likes
0
3265
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:07 AM . Last Modified: ‎2024-03-20 12:23 AM

Let me double check with SecretSquirrel tomorrow. He will know more than I think you'll get out of tech support to be completely honest and both he and I are out of the office today.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-30 12:07 AM . Last Modified: ‎2024-03-20 12:23 AM

0 Likes
0
3265
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:07 AM . Last Modified: ‎2024-03-20 12:23 AM

We are a little confused, how is the UTS panel powered if the breaker at your panel is off?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 12:07 AM . Last Modified: ‎2024-03-20 12:23 AM

0 Likes
0
3265
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:07 AM . Last Modified: ‎2024-03-20 12:23 AM

sorry I haven't been very clear.   I've applied power to circuits 9/10 b/c they are dedicated to the AC unit.   All the other circuits are currently not terminated so I have the breakers off.  Last time all the breakers were on when I ran the unit so I guess I don't know if the output issue is because of the breaker being off for the circuit and the "no output" is the correct error code when a breaker is turned off.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-30 12:08 AM . Last Modified: ‎2024-03-20 12:23 AM

0 Likes
0
3265
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:08 AM . Last Modified: ‎2024-03-20 12:23 AM

Yes, we believe it is normal what you're seeing until it is brought online based on what we can tell. I don't think we'll be able to verify operation 100% until the breakers are on.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 12:08 AM . Last Modified: ‎2024-03-20 12:23 AM

0 Likes
0
3265
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:08 AM . Last Modified: ‎2024-03-20 12:23 AM

yes, it appears you are correct.   As I've been terminating all my connections on each circuit and flipping the breaker and resetting the unit, the flashing circuits and no output faults go away!   However I still have an issue with my #8 circuit.   There is no light on what so ever but all the other lights are solid red indicating no problems.   The one thing I'm wondering is that I have this going to surge protecting breaker.   I haven't tried to swap it out to see if that causes the light to turn on but there is no error message, it just doesn't have a light and there is no power going to the circuit...

Any ideas?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-30 12:08 AM . Last Modified: ‎2024-03-20 12:23 AM

0 Likes
0
3265
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:08 AM . Last Modified: ‎2024-03-20 12:23 AM

Is it a GFCI or AFCI? The UTS won't work with them because they need isolated neutrals but the UTS shares the neutral throughout the unit.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 12:08 AM . Last Modified: ‎2024-03-20 12:23 AM

0 Likes
0
3265
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:08 AM . Last Modified: ‎2024-03-20 12:23 AM

It is a circuit surge protector breaker...  however tonight I tried swapping it with a regular breaker and it did the same thing after I reset to default factory settings.   The unit goes through a system check for each circuit and when it gets to 8 the light goes off.   I finally just bypassed the UTS system and did a direct connection and the circuit powers fine.   For whatever reason the circuit 8 isn't getting power.   I've changed the fuse, checked the wire connections, used different breakers....  Is there a setting that would be an issue?   I don't see how that would be possible being that I keep factory defaulting when I make a change.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-30 12:08 AM . Last Modified: ‎2024-03-20 12:23 AM

0 Likes
0
3265
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:08 AM . Last Modified: ‎2024-03-20 12:23 AM

I don't think it is a setting, especially since you reset it to defaults. I checked on my end with to see if there was anything you missed and at this point, we don't see what else it could be beyond the breakers, wires, fuse, etc. We're thinking an RMA may be in order unfortunately undecided

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 12:08 AM . Last Modified: ‎2024-03-20 12:23 AM

0 Likes
0
3265
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:08 AM . Last Modified: ‎2024-03-20 12:23 AM

I was afraid of that.   I'll probably just not have the number 8 circuit as the pain to uninstall and RMA is probably not worth the effort.   Thanks again for all the help and I appreciate the assistance very much!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-30 12:08 AM . Last Modified: ‎2024-03-20 12:23 AM

0 Likes
0
3265
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:08 AM . Last Modified: ‎2024-03-20 12:23 AM

You're welcome. Let us know if anything else changes or you have further questions.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.