Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84506members
353725posts

UPS with Alarm Suppression

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

Solved
raymondzachary_apc
Cadet
0 Likes
1
100

UPS with Alarm Suppression

This was originally posted on APC forums on 5/9/2009


I am looking for a UPS of any Brand or Capacity that has a hardware switch to turn of the audible alarm after it notifies me that something is wrong. I would accept a system that just does its job and tells me nothing at all until I want to know. I do not require a lot of sophistication. I just want to keep telephones and credit card machine up and running. Computer protection would be nice but is not a priority. What is a priority is QUIET.

Thanks for any help you can offer.

Raymond Zachary


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
100

Re: UPS with Alarm Suppression

This reply was originally posted by Angela on APC forums on 5/11/2009


hi raymond..

depending on what you need size wise, most of APC's UPSs allow for the alarms to be disabled via software. there arent any UPSs that have a switch on them to disable the alarm permanently though, its always in the software to be disabled permanently.

You can order a Smart UPS with X-option 413 which would have a 2-4 week lead time but any Smart UPS that ends with "X413" would come with the alarm disabled. you could always turn it on via the software too but at least this wouldn't require you to do it when you first got the UPS.

lastly, just to note, [reference this article for audible alarms that can never be disabled|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=6789].

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
101

Re: UPS with Alarm Suppression

This reply was originally posted by Angela on APC forums on 5/11/2009


hi raymond..

depending on what you need size wise, most of APC's UPSs allow for the alarms to be disabled via software. there arent any UPSs that have a switch on them to disable the alarm permanently though, its always in the software to be disabled permanently.

You can order a Smart UPS with X-option 413 which would have a 2-4 week lead time but any Smart UPS that ends with "X413" would come with the alarm disabled. you could always turn it on via the software too but at least this wouldn't require you to do it when you first got the UPS.

lastly, just to note, [reference this article for audible alarms that can never be disabled|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=6789].