Hi folks,
I have some problem with my APC CS 350.(BK350EI) sn:NB0643008777 It is a 5-6 years old unit worked fine. A week ago the Replace battery sign came up, the red light is flashing. I checked the battery it had 8V so it was bad. I bought a new one for it. Installed it and the red light is still blinking. (I have continuously on-Line light too)
Any Idea what could I do?
Thx:Peter
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:54 PM . Last Modified: 2024-03-21 01:26 AM
Peter,
A flashing replace battery indicator on the UPS means that the UPS is unable to detect a battery. This could be caused by a bad or the UPS itself, unfortunately on your case it shows that the culprit is the unit already.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:54 PM . Last Modified: 2024-03-21 01:26 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:54 PM . Last Modified: 2024-03-21 01:26 AM
Hi,
Thank for your infos and suggestions. I will try asap and will make a
report back...
Thx
Peter
2013.03.05. 18:14, "SecretSquirrel" <
apc-admin@apc-forums-phx.hosted.jivesoftware.com> ezt írta:
**
APC Community Homepage <> APC
CS350 Replace battery light with new battery created by SecretSquirrel<>in
Computer & Peripheral UPS or Surge - View the full discussion<>
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:54 PM . Last Modified: 2024-03-21 01:26 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:54 PM . Last Modified: 2024-03-21 01:26 AM
Hi folks,
I have some problem with my APC CS 350.(BK350EI) sn:NB0643008777 It is a 5-6 years old unit worked fine. A week ago the Replace battery sign came up, the red light is flashing. I checked the battery it had 8V so it was bad. I bought a new one for it. Installed it and the red light is still blinking. (I have continuously on-Line light too)
Any Idea what could I do?
Thx:Peter
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:54 PM . Last Modified: 2024-03-21 01:26 AM
Peter,
A flashing replace battery indicator on the UPS means that the UPS is unable to detect a battery. This could be caused by a bad or the UPS itself, unfortunately on your case it shows that the culprit is the unit already.