Hi Larry,
By default, the self-test is run each time the UPS is started and then every 14 days after that.
You could run a self-test on each system so they would be in sync. The drawback is that if the UPS is restarted, you must re-sync when the remainder run their test.
A solution is to set the test to never and set a reminder to run the test manually or run via SSH or SNMP scripting. Using SSH/CLI the command is UPS -s start.