Posted: 2023-03-09 06:07 PM
Hi, Ive got an older UPS with an AP9537SUM
Its running SUMX and AOS v6.9.4 but browsers still wont connect via HTTPS
Does anyone know if further changes around TLS are resolved in newer firmware.
If so the closest firmware i can find is :
UPS Network Management Card v7.0.8 Firmware for Smart-UPS & Galaxy 3500 with AP9630/31/35
Firmware Upgrades for all supported APC offers, bringing the latest supported features to end users.
SFSUMX708
I fund elsewhere in the forum that APC963x firmware is good for the AP9537SUM, but it was an older post. Just wondering if the firmware I have found there should be good.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-03-09 06:47 PM
Answered my own question by reading the manual:
metra application firmware v7.0.8 release notes apply to the following NMC cards:
The Smart-UPS and single-phase Sym• AP9630 (CH) UPS Network Management Card 2
• AP9631 (CH) UPS Network Management Card 2
• AP9635 (CH) UPS Network Management Card 2
• Single-Phase UPS models with an integrated Network Management Card 2 – AP9537SUM
(e.g. All Smart-UPS SRT models 5kVA and above)
Have applied firmware, and deleted/regenerated the self signed cert and HTTPS working normally now.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-03-09 06:47 PM
Answered my own question by reading the manual:
metra application firmware v7.0.8 release notes apply to the following NMC cards:
The Smart-UPS and single-phase Sym• AP9630 (CH) UPS Network Management Card 2
• AP9631 (CH) UPS Network Management Card 2
• AP9635 (CH) UPS Network Management Card 2
• Single-Phase UPS models with an integrated Network Management Card 2 – AP9537SUM
(e.g. All Smart-UPS SRT models 5kVA and above)
Have applied firmware, and deleted/regenerated the self signed cert and HTTPS working normally now.