BACK UPS PRO 1200 / 1500 230V - BATTERY PROBLEM

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • BACK UPS PRO 1200 / 1500 230V - BATTERY PROBLEM
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
123
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:52 PM . Last Modified: ‎2024-03-21 01:30 AM

0 Likes
2
1631
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:52 PM . Last Modified: ‎2024-03-21 01:30 AM

BACK UPS PRO 1200 / 1500 230V - BATTERY PROBLEM

Hi my name is Kushtrim, i have bought a brand new back ups apc pro 1200 / 1500 but i have a problem, my apc wont recognize my battery,
dont know what to do i have let my ups for about 1 day to recharge but when i turned my ups on same problem the battery was still low, and it show's me on display the battery flashing / ,
i wonder how this can be because my ups and battery is brand NEW 😞



Wat could be the problem :S please help !!!



Thank you! 😞

Message was edited by: Morrzy

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • apc
  • back-ups
  • battery
  • battery-low
  • beeping
  • brand-new
  • communicationg
  • flashing
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:52 PM . Last Modified: ‎2024-03-21 01:30 AM

0 Likes
0
1631
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:52 PM . Last Modified: ‎2024-03-21 01:30 AM

can you give us the first several digits of the serial number? do you happen to have a voltmeter available to measure the DC voltage on the battery?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:52 PM . Last Modified: ‎2024-03-21 01:30 AM

0 Likes
0
1632
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:52 PM . Last Modified: ‎2024-03-21 01:30 AM

can you give us the first several digits of the serial number? do you happen to have a voltmeter available to measure the DC voltage on the battery?

Reply

Link copied. Please paste this link to share this article on your social media post.

Joev156
Joev156
Cadet

Posted: ‎2023-03-07 03:53 PM

0 Likes
0
1457
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-07 03:53 PM

Hi, i acquired a new unit from Amazon on the 4th June 2019 - £293. I have already had to change the batteries once and acquired a spare set just in case as it seems to want new ones every 2 to 3 years. 

However, i was working away from the office over the last two days where access to my sever (supplied by power from the APC Pro 1200) was working well until earlier today before I returned to the office. I was unable to remotely access my server from the laptop or mobile phone leading me to believe something was wrong with the server itself.

Upon returning to the office, I noticed that everything that was connected to the UPS was off and that the UPS itself had turned off, explaining why i the server had suddenly stopped working - no power to anything, including the UPS itself..

I replaced the batteries this evening eager to get on with what i had to complete before tomorrow but the unit beeps only when pressing the on-off button after replacement and it wont turn on. I tried another set of batteries and nothing seems to work. 

I cannot fully accept that all of the batteries can have failed at the same time and even with a new set in and power cord connected, it wont turn on and simply beeps at me. 

The old Back-Ups CS 650 with a single battery serving another office PC, comms, internet, etc. seems to be working fine and has done for a number of years now. This new one seems to have failed after just over three and a half years.

Is there anything I have dont wrong and is there a solution to what might be a common and easy-fix problem? 

I hope there is but if it turns out that i need a replacement, it might not be another APC this time around...

Desperately seeking some assistance. 

Many thanks

Joev156

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore