UPS Pro 550 - Problem with Synology DS2411+

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • UPS Pro 550 - Problem with Synology DS2411+
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
123
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 07:38 AM . Last Modified: β€Ž2024-03-21 04:47 AM

0 Likes
5
1663
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 07:38 AM . Last Modified: β€Ž2024-03-21 04:47 AM

UPS Pro 550 - Problem with Synology DS2411+

Hi,

I use a UPS Pro 550 with a Synology DS2411+ NAS. The units are Connectet with the USB Cable, The NAS recognice the USV.

If i remove the Power Cable from the UPS the DS2411+ stops and shut down. - OK
If i stick in the Power Cable to the UPS the DS2411+ starts up. - OK

But then the UPS switches to Batterie Mode (Klack and I see it on the UPS Display) and shut down again.(Unsave)
After the next Start up everthing is OK.

Is it possible that the DS2411 switch the UPS to Batterie Mode with the USB Cable, or is it a Firmeware BUG from the UPS??
I looked in the USV with the SW on the PC but there is no Point where i can adjust this.

thanks for Help!

Edit: It looks like, it's the Firmware from the APC UPS - i read a similar Problem with a PC at an other tread here, and in the List from Synology. From Synology i got the Info, that the DS2411+ does not send to the APC USP that it should switch to batterie Mode.
So i don't understand this Function from The APC UPS - for me this is a Bug.

Message was edited by: JoGi65

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 07:38 AM . Last Modified: β€Ž2024-03-21 04:47 AM

0 Likes
0
1663
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 07:38 AM . Last Modified: β€Ž2024-03-21 04:47 AM

its very difficult to say where the problem is but in APC's defense, i cannot find anywhere stating that this UPS (or any UPS) supports this type of NAS? Does the manufacturer have a supported UPS list where APC UPSs are listed or recommended (but don't work)? I don't think APC has tested many NAS or any for that matter to ensure compatibility so it seems as though we are being blamed for this problem not knowing that this is something users are using the device for and are being told to purchase this model.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 07:38 AM . Last Modified: β€Ž2024-03-21 04:47 AM

0 Likes
0
1663
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 07:38 AM . Last Modified: β€Ž2024-03-21 04:47 AM

Hi Johannes,

There is a lot of factors that we need to look at with your situation. These factors are outlined on this kbase [Equipment connected to a Back-UPS product turns off unexpectedly and/or reboots.|http://nam-en.apc.com/app/answers/detail/a_id/20/kw/equipment%20reboots]. It seems that the NAS is having an issue with either the transfer time or the step approximated sine wave that the UPS provides when it is running on battery.

Have you tried contacting your NAS manufacturer and check with them the transfer time that it accepts and if it would run on a step approximated sine wave? Our BackUPS product line has an 4 to 6ms of transferring from Online to On Battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 07:38 AM . Last Modified: β€Ž2024-03-21 04:47 AM

0 Likes
0
1663
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 07:38 AM . Last Modified: β€Ž2024-03-21 04:47 AM

So i read all the factors of the kbase. No one from them is useable for me.

The Transfer Time is not the Problem, because when i don't shut down the APC UPS with the NAS Firmware it works. Also it works right, when i wait, until the Batterie Power from the APC USV is emtpy. Than everthing, safe Shutdown and Startup!!, are right!
Also the Step approximated sine wave is not the Problem. The NAS works with Batterie Power, where the Step approximated sine wave is in use. Also it Starts up right, when i wait until the Batterie Power is empty, ore the Power 230V comes back before the Batterie is empty.

Only when I shut down the APC UPS with the NAS Firmware (Shut down is safe and ok), then by the Start up when 230V are back, the APC UPS switches itself to Batterie Mode after 30 or 60 sec. the APC UPS shut down again! (Itself an so clerly also the NAS πŸ˜‰ (Power 230V are here and ok!) And then at the next Start, witch make the APC UPS from itself, it stays online.

And I asked Synology and the sayed i should buy a other UPS. They also sayed, that the NAS don't send a Signal after Start up that the APC UPS should switch to Battery Mode and shut down unsafe.
I don't understand how the APC UPS can switch to Batterie Mode after start up! when the Power is online (230V). How is this possible?

The Problem is reproducible every time, and i have no Chance after Shut down from the APC UPS with the NAS Firmware (Same as in your SW) to start up the APC UPS without a second Shutdown.

So i think, the Start Up routine from the APC UPS is the Problem! (Only after Shut down APC UPC with the Client order)
And sorry that i can say you exactly the switch of times or switch to Batterie mode Time from the APC, because i don't want to crash my Raid with 7 HDD'S on the NAS, because now they are full with Data. To Rebuild it, it's a looong Time.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 07:38 AM . Last Modified: β€Ž2024-03-21 04:47 AM

0 Likes
0
1663
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 07:38 AM . Last Modified: β€Ž2024-03-21 04:47 AM

For your Info:
I heard from a other Synology User, that the "APC Back-UPS ES 550VA, USB (BE550G-GR)" has this Problem i descriped, not.
So it looks like the cheaper Part is better.
Can anyone explane me why?
Can I change the FW from the APC UPC?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 07:38 AM . Last Modified: β€Ž2024-03-21 04:47 AM

0 Likes
0
1663
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 07:38 AM . Last Modified: β€Ž2024-03-21 04:47 AM

Yes, I have the same problem with APC Back-UPS ES 550VA, USB BE550G-GR , and Synology DS413j . I think the fw from ups is the problem. I do not know what to do!?! I do not recommend this product  APC Back-UPS ES 550VA, USB BE550G-GR because: has too many eco features, power management stuff for conserving the energy, but finally the ups not doing the job. Disappointed...

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 07:38 AM . Last Modified: β€Ž2024-03-21 04:47 AM

0 Likes
0
1664
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 07:38 AM . Last Modified: β€Ž2024-03-21 04:47 AM

its very difficult to say where the problem is but in APC's defense, i cannot find anywhere stating that this UPS (or any UPS) supports this type of NAS? Does the manufacturer have a supported UPS list where APC UPSs are listed or recommended (but don't work)? I don't think APC has tested many NAS or any for that matter to ensure compatibility so it seems as though we are being blamed for this problem not knowing that this is something users are using the device for and are being told to purchase this model.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore