UPS Compensating for high input voltage

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • UPS Compensating for high input voltage
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
119
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:03 AM . Last Modified: ‎2024-03-26 03:42 AM

0 Likes
1
21059
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:03 AM . Last Modified: ‎2024-03-26 03:42 AM

UPS Compensating for high input voltage

Howdy,

I have a SMX2200HV UPS that is constantly giving me a "Compensation for high input voltage" alarm. I have changed the sensitivity of the UPS to low in the hope that it can take a bit more of a pounding but its still not very happy. The UPS is currently powered off a generator as it is located in a very remote part of Australia and the voltage is obviously not very stable. What is the input voltage tolerance that this UPS can take before it starts causing problems? There is no getting away from this fluctuating power at this site so is there anything i can do to this UPS to make it a bit more resilient? Any works to improve the input power would be difficult due to its remoteness but we were thinking that a ac power filter may be the only option. 

I have attached a snippet of the log showing the input voltage all over the place. Any suggestions would be great!

Cheers 😛 

Attachments
Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • apc
  • battery
  • failure
  • smx2200hv
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:04 AM . Last Modified: ‎2024-03-26 03:42 AM

0 Likes
0
21052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:04 AM . Last Modified: ‎2024-03-26 03:42 AM

Hi Marc

I imagine you have done all you can (input voltage set to 240v, sensititvity set to poor, and high transfer point set accordingly) as you are getting the Compensation for high input voltage level which means the AVR is cutting the voltage down as close as it can get to the set input voltage( it can reduce the voltage by 15%), otherwise you would see the UPS going on and off battery.

 

Looking at the manual it is capable of handling 276V and reducing it to 235 V with AVR. Above that the UPS will go on battery.

 

tm2%2BsOQcUkVtzO4zqpcBWA%3D%3D.pngtm2%2BsOQcUkVtzO4zqpcBWA%3D%3D.png

Whilst you don't have the ideal situation,looking at the data log you've provided,  the UPS is capable of supplying your load with a stable ouput voltage with a few occurences of going on to battery, which may be avoided by upping the High Transfer point up another level.

 

Regards

 

Matt

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:04 AM . Last Modified: ‎2024-03-26 03:42 AM

0 Likes
0
21053
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:04 AM . Last Modified: ‎2024-03-26 03:42 AM

Hi Marc

I imagine you have done all you can (input voltage set to 240v, sensititvity set to poor, and high transfer point set accordingly) as you are getting the Compensation for high input voltage level which means the AVR is cutting the voltage down as close as it can get to the set input voltage( it can reduce the voltage by 15%), otherwise you would see the UPS going on and off battery.

 

Looking at the manual it is capable of handling 276V and reducing it to 235 V with AVR. Above that the UPS will go on battery.

 

tm2%2BsOQcUkVtzO4zqpcBWA%3D%3D.pngtm2%2BsOQcUkVtzO4zqpcBWA%3D%3D.png

Whilst you don't have the ideal situation,looking at the data log you've provided,  the UPS is capable of supplying your load with a stable ouput voltage with a few occurences of going on to battery, which may be avoided by upping the High Transfer point up another level.

 

Regards

 

Matt

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore