SRT1500RMXLA doesn´t recognize the SMX48RMBP2V external battery pack

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • SRT1500RMXLA doesn´t recognize the SMX48RMBP2V external battery pack
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
121
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
Start a Topic
robmir_apc
Lieutenant robmir_apc
Lieutenant

Posted: ‎2024-07-13 05:09 AM . Last Modified: ‎2024-07-13 06:20 AM

0 Likes
3
679
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-13 05:09 AM . Last Modified: ‎2024-07-13 06:20 AM

SRT1500RMXLA doesn´t recognize the SMX48RMBP2V external battery pack

Hi Bill and hope you are fine: this question is for you !!!!!   Since my wife´s MacMini after it´s  latest firmware update doesn´t like the threshold of our SMX1000 when switching from A/C to battery and turns off right away   I bought a dual conversion SRT1500RMXLA to replace it and was expecting to hook to it the 3 SMX48RMBP2V external battery I had hooked to the older SMX1000 since this double conversion UPS has the same type off 48 Volt blue 4 pin conector  and unfortunately this UPS doesn´t recognize them. 

I was checking the recommended SRT48RMBP and believed you only designed it to use the same type of battery cartridge as the SRT1500 but it seems you also changed something on the external battery sensing logic.

Is there a way as to trick the SRT1500 to recognize the  SMX external  battery packs series ?

 

By the way which is the SRT1500RMXLA front bezel  replacement part number ? The screen display is bigger so an SMX bezel doesn´t fit at all !!!

Labels
  • Labels:
  • Home & Office - UPS & Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Teken
Kirk Teken
Kirk

Posted: ‎2024-10-15 05:12 AM . Last Modified: ‎2024-10-15 05:14 AM

0 Likes
2
669
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-15 05:12 AM . Last Modified: ‎2024-10-15 05:14 AM

I swear this exact question was posed and answered by me this year?!? 🤔

 

Regardless, the SMX Series uses a simple resistor network to inform the system how many extended battery packs are present.

 

The SRT Series uses a combination of resistor and a IC to determine if an extended battery pack is present, serial firmware, temperature, battery health etc.

 

The SRT Front Bezel: 0M-77876

 

Guess you made a duplicate post:

 

https://community.se.com/t5/APC-UPS-for-Home-and-Office-Forum/SRT1500-Doesn-t-recognize-external-SMX...

Reply

Link copied. Please paste this link to share this article on your social media post.

robmir_apc
Lieutenant robmir_apc
Lieutenant

Posted: ‎2024-10-16 03:08 AM

In response to Teken
0 Likes
1
644
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-16 03:08 AM

Thanks, I got you the first time so I don´t understand why the question was duplicated đꤔ

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2024-10-16 03:14 AM

In response to robmir_apc
0 Likes
0
643
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-16 03:14 AM

Probably a glitch in the Matrix 🤣

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore