Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback β Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: β2024-10-11 03:43 AM
My APC UPS SRVP10KIL fell from the battery cage and shut down, I have done some checks, discovered no issues, ye the system is not coming ON. How do I resolve this please?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2024-10-11 05:56 AM
Based on what you stated up above the unit is obviously damaged. π€¦ββοΈ
Regardless, does the system power on? What LED / LCD indicators are present if at all?
Does the system make any sounds (beeps) now or relay clicks upon power up?
What is the current status of the power cord, battery connector, breaker?
Does this system have a EPO Protection Circuit connected to the system?!?
Provide the answers and photo of the unit top, bottom, sides, for review. π
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2024-10-15 02:21 AM
The machine was completely idle, I have worked on the power board that got the power restored, but no voltage output
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2024-10-15 03:02 AM
What are the answers to my questions up above?!?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2024-10-16 05:42 AM
Yes, the machine powers on now
All the LCD indicators are present
There's a beep and constant relay clicks
The power cords, battery connector and breaker are all fine


Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2024-10-17 07:11 AM
Speaking from an insurance / ISO / cUL position the hardware should be decommissioned and written off.
As it no longer meets any requirements relating to safety, electrical conformity, and manufacture specifications.
If the hardware is still under APC Warranty you could submit a RMA to see if the equipment can be repaired / replaced.
Regardless, this is a hard lesson to learn a UPS must be properly secured and mounted. π€¦ββοΈβΉοΈ
Let us know what happens and what you decide to do. π
Link copied. Please paste this link to share this article on your social media post.
Youβve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.